I haven't seen any in over 50 years. Of course, I have only been 
paying attention for the last 27.



At 06:30 PM 3/18/2009, you wrote:
>In my 26 years in the Industry I have never installed one in the 
>closed meter loop or designed one with a check valve. Why would NFPA 
>'Pumps for Fire Protection Sytems' by Kenneth E. Isman, P.E. & 
>Milosh T. Puchovsy, P.E. state that.
>
>
>
>
>
>
>
>George Medina Jr.
>Sr. Fire Sprinkler Designer
>95-1015 Ka'apeha Pl.
>Mililani, HI 96819
>808-388-5974 CL#
>
>
>-----Original Message-----
>From: Don Lowry <[email protected]>
>To: [email protected]
>Sent: Wed, 18 Mar 2009 12:43 pm
>Subject: RE: Check Valve On Discharge side of Flow Meter
>
>
>
>Perhaps your speaking of a check valve is required on the
>discharge side of the FP.  The meter loop just circulates
>water back to the pump and shouldn't have anything to do
>with city supply.  Look at the example configuration in the
>appendix for your locations of checks required.  As far as
>the text, I don't have NFPA-20 (2002) we still use 99.
>Personally I have never used or seen a check valve on the
>meter loop in 30+ years.
>
>Don Lowry,
>Dickerson Fire Protection
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf
>Of George Medina Jr
>Sent: Wednesday, March 18, 2009 3:04 PM
>To: [email protected]
>Subject: Check Valve On Discharge side of Flow Meter
>
>NFPA No.:Z4Pump02 page 108 - States that a check valve is
>required on the discharge side of flow meter. Our union
>field guys state they never put one on?there. Is this
>correct?
>I believe a flow meter would be damaged from positive city
>pressure back flowing through the meter after shutting down
>the pump and before closing the isolation valve. Somebody
>correct me for being wrong.
>
>
>George Medina Jr.
>Sr. Fire Sprinkler Designer
>Dorvin D. Leis Inc.
>Honolulu, HI 96819
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerfor
>um
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to