I had not been following the thread because the subject title hasn't 
changed, but am I correct in assuming this problem does not occur with 
pressure switches at the top of retard chambers?
 
James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





Jay Jay Blocker <[email protected]>
Sent by:  [email protected]
03/03/2009 08:09 PM
Please respond to sprinklerforum

To
[email protected]
cc

Subject
Re: statistics







Rodney i do not believe you are a nut im just not sure we are looking at 
the same equipment.  Maybe no one else is admitting this is a problem 
because it may not be.  I say that to say this.
Lets look at basic common science here.  If you have a flow switch set at 
76 seconds and an air pocket tripped it that would suggest that there was 
enough air  in one single pocket to not only move the paddle but hold it 
in the activated position.  THis would mean the velocity of the air would 
have to have enough force to over power the spring and hold it for 76 
seconds.  None moving air could not perform this action.  So if there is a 
pocket of air that can do this i do not believe moving the ITC would 
help.  I would have to work with the water dept. and find a way to prevent 
these air pockets from entering the system.  Maybe even check with 
businesses near bye the affected buildings and see if there domestic water 
has had any problems.  I dont see how air pockets would discriminate 
between systems (honestly seems like the domestic would be more 
susseptible to this problem).  Im not saying your wrong i am just really 
lost as to how this
 could happen.  Have you tied changing out the flow switch?

Jay 




________________________________
From: Rodney Hamm <[email protected]>
To: [email protected]
Sent: Tuesday, March 3, 2009 3:26:47 PM
Subject: Re: statistics

Jay,

It is really not a "theory" at this point. I have found this problem at so
many locations and resolved the issue that I am absolutely convinced the
large trapped air pockets are causing the false alarms. 

I have placed my digital LPT Data Logger on the downstream side of wet
systems and recorded the system pressure on 30 second intervals for 7 day
periods. The graph shows the gradual pressure increases/decreases caused 
by
temperature changes and the exact time of the false fire alarms are always
indicated by a distinct pressure increase which lasts for more than 60
seconds. This happens when the water supply increases at the same time as 
a
cold front (or significant drop in temperature). Public water supply 
systems
typically fill gravity tanks at night and temperature changes usually drop
at night during Spring and Fall (this is typically the time of year these
false alarms are most common). I use the weather channel to determine the
greatest temperature drop on the night when the false fire alarm occurred.

After I bleed as much air from the system as possible, the LPT Data Logger
verifies that the pressure fluctuations are much less severe and the false
fire alarms are a thing of the past.

I have one customer where this problem occurred when there was a 
temperature
drop and the jockey pump filled the system EVEN WITH THE DELAY ON THE FLOW
SWITCH SET AT 76 SECONDS! After we bled the air from the system, the 
problem
was resolved. LPT Data Logger was also used on this system. Yes that is
correct same problem even with a fire pump......the jockey pump at this
facility typically requires 20-25 seconds to start/stop, but when the
underground main pressure is just right and the air pocket/temperature 
issue
combines.......we had false fire alarms. I checked the electronic water 
flow
switch 7-8 times and the delay was always between 70-80 seconds!

In summary, air will expand and contract with temperature changes while
water will not. All system have some air, but systems with a significant
percentage/volume of air will allow water to flow into the system to
equalize the system pressure when the pressure downstream of the alarm 
check
valve drops below the upstream pressure. When the time required to 
replenish
the system exceeds the flow switch delay.....the fire alarm will activate.
It is even more common for systems which have pressure switches on the
retard chambers.

The flow switch cycling issue is also a huge problem in some instances!
Refer to my previous post regarding the typical test method used by alarm
technicians.

I sincerely hope this helps. I imagine some of the people on this forum
think I am a freak'n nut. I'm really not crazy! I will admit that I seem a
little obsessed with this issue, but I am getting tired of finding the
problem and none of my buddies in the Fire Sprinkler Industry want to 
admit
this is an issue. It has become a bit of a pet-peeve of mine I suppose.

Take care, 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677
Cell  (478) 396-6988

-----Original Message-----
Date: Mon, 2 Mar 2009 17:07:39 -0800 (PST)
From: Jay Jay Blocker <[email protected]>
Subject: Re: statistics
To: [email protected]
Message-ID: <[email protected]>
Content-Type: text/plain; charset=iso-8859-1

Rodney could you please elaborate on your theory of the air pocket 
tripping
the flow switch. Several of us in my office are baffled.

Jay


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to