Yes Jim.  Pressure in the retard chamber is relieved through the drain when
the alarm port is closed.

On Fri, Mar 20, 2009 at 10:26 AM, <[email protected]> wrote:

> I had not been following the thread because the subject title hasn't
> changed, but am I correct in assuming this problem does not occur with
> pressure switches at the top of retard chambers?
>
> James L.(Jim) Roberts, PE/SET
> Fluor Corporation
> 100 Fluor Daniel Drive - C104F
> Greenville, SC 29607
> 864.281.5149
> 864.281.4916(Fax)
>
>
>
>
>
> Jay Jay Blocker <[email protected]>
> Sent by:  [email protected]
> 03/03/2009 08:09 PM
> Please respond to sprinklerforum
>
> To
> [email protected]
> cc
>
> Subject
> Re: statistics
>
>
>
>
>
>
>
> Rodney i do not believe you are a nut im just not sure we are looking at
> the same equipment.  Maybe no one else is admitting this is a problem
> because it may not be.  I say that to say this.
> Lets look at basic common science here.  If you have a flow switch set at
> 76 seconds and an air pocket tripped it that would suggest that there was
> enough air  in one single pocket to not only move the paddle but hold it
> in the activated position.  THis would mean the velocity of the air would
> have to have enough force to over power the spring and hold it for 76
> seconds.  None moving air could not perform this action.  So if there is a
> pocket of air that can do this i do not believe moving the ITC would
> help.  I would have to work with the water dept. and find a way to prevent
> these air pockets from entering the system.  Maybe even check with
> businesses near bye the affected buildings and see if there domestic water
> has had any problems.  I dont see how air pockets would discriminate
> between systems (honestly seems like the domestic would be more
> susseptible to this problem).  Im not saying your wrong i am just really
> lost as to how this
>  could happen.  Have you tied changing out the flow switch?
>
> Jay
>
>
>
>
> ________________________________
> From: Rodney Hamm <[email protected]>
> To: [email protected]
> Sent: Tuesday, March 3, 2009 3:26:47 PM
> Subject: Re: statistics
>
> Jay,
>
> It is really not a "theory" at this point. I have found this problem at so
> many locations and resolved the issue that I am absolutely convinced the
> large trapped air pockets are causing the false alarms.
>
> I have placed my digital LPT Data Logger on the downstream side of wet
> systems and recorded the system pressure on 30 second intervals for 7 day
> periods. The graph shows the gradual pressure increases/decreases caused
> by
> temperature changes and the exact time of the false fire alarms are always
> indicated by a distinct pressure increase which lasts for more than 60
> seconds. This happens when the water supply increases at the same time as
> a
> cold front (or significant drop in temperature). Public water supply
> systems
> typically fill gravity tanks at night and temperature changes usually drop
> at night during Spring and Fall (this is typically the time of year these
> false alarms are most common). I use the weather channel to determine the
> greatest temperature drop on the night when the false fire alarm occurred.
>
> After I bleed as much air from the system as possible, the LPT Data Logger
> verifies that the pressure fluctuations are much less severe and the false
> fire alarms are a thing of the past.
>
> I have one customer where this problem occurred when there was a
> temperature
> drop and the jockey pump filled the system EVEN WITH THE DELAY ON THE FLOW
> SWITCH SET AT 76 SECONDS! After we bled the air from the system, the
> problem
> was resolved. LPT Data Logger was also used on this system. Yes that is
> correct same problem even with a fire pump......the jockey pump at this
> facility typically requires 20-25 seconds to start/stop, but when the
> underground main pressure is just right and the air pocket/temperature
> issue
> combines.......we had false fire alarms. I checked the electronic water
> flow
> switch 7-8 times and the delay was always between 70-80 seconds!
>
> In summary, air will expand and contract with temperature changes while
> water will not. All system have some air, but systems with a significant
> percentage/volume of air will allow water to flow into the system to
> equalize the system pressure when the pressure downstream of the alarm
> check
> valve drops below the upstream pressure. When the time required to
> replenish
> the system exceeds the flow switch delay.....the fire alarm will activate.
> It is even more common for systems which have pressure switches on the
> retard chambers.
>
> The flow switch cycling issue is also a huge problem in some instances!
> Refer to my previous post regarding the typical test method used by alarm
> technicians.
>
> I sincerely hope this helps. I imagine some of the people on this forum
> think I am a freak'n nut. I'm really not crazy! I will admit that I seem a
> little obsessed with this issue, but I am getting tired of finding the
> problem and none of my buddies in the Fire Sprinkler Industry want to
> admit
> this is an issue. It has become a bit of a pet-peeve of mine I suppose.
>
> Take care,
>
> Rodney K. Hamm, P.E.
> President/Owner
> Falcon Fire Protection
> Office  (478) 953-1677
> Cell  (478) 396-6988
>
> -----Original Message-----
> Date: Mon, 2 Mar 2009 17:07:39 -0800 (PST)
> From: Jay Jay Blocker <[email protected]>
> Subject: Re: statistics
> To: [email protected]
> Message-ID: <[email protected]>
> Content-Type: text/plain; charset=iso-8859-1
>
> Rodney could you please elaborate on your theory of the air pocket
> tripping
> the flow switch. Several of us in my office are baffled.
>
> Jay
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> ------------------------------------------------------------
> The information transmitted is intended only for the person
> or entity to which it is addressed and may contain
> proprietary, business-confidential and/or privileged material.
> If you are not the intended recipient of this message you are
> hereby notified that any use, review, retransmission, dissemination,
> distribution, reproduction or any action taken in reliance upon
> this message is prohibited. If you received this in error, please
> contact the sender and delete the material from any computer.
>
> Any views expressed in this message are those of the individual
> sender and may not necessarily reflect the views of the company.
> ------------------------------------------------------------
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to