Don,

The heat tracing for branch lines have to listed.  The heat tracing is  
not listed yet.  We did a Technical Update last August on this  
subject.  See below 3rd paragraph.

Tom Wellen - AFSA



We have a building with an unheated attic space of approximately 3,900  
square feet. The project specifications are requiring a wet fire  
protection system with the piping to be insulated and heat traced to  
prevent freezing. Is it the intent of Section 8.16.4.1 to allow this  
method of freeze protection for an entire system in lieu of a dry type  
system? Would sprinkler heads be protected from freezing by heat  
tracing branch line piping?"

We have reviewed the 2007 edition of NFPA 13 as the applicable  
standard. Our informal interpretation is that heat tracing is  
permitted in lieu of a dry pipe system but heat trace products are not  
yet available for branch line applications.

A manufacturer has reported that there is no heat tracing cable  
available with a listing for branch lines since the testing procedures  
have not yet been developed or defined by FM or UL. UL has been  
contacted and they confirmed that there is not yet a test standard and  
that a significant amount of work must be completed on the ANSI  
standard before testing can begin. A time estimated completion date  
has not yet been identified.

The heat tracing will affect the sprinklers thus the testing standard  
will have to address this issue. The concern is that the tracing wire  
may overheat the branch line and activate the sprinkler. The current  
UL listing is for use on piping between the system control valve and  
the system branch lines, but does not include the branch lines. Thus a  
dry pipe or antifreeze system should be installed for attic space  
unless the space is heated above 40 degrees F where a wet pipe system  
could be installed.




On Mar 24, 2009, at 10:35 AM, Don Lowry wrote:

> What is the main reason we cannot insulate and heat strip
> Branch lines,  I have always pointed out to every owner, AHJ
> and engineer that it is "unacceptable practice" per
> standard, however several authorities here in Texas have
> been allowing and encouraging this practice.  I need to give
> them a good reason other than the standard says so.  The
> handbook doesn't quite explain this.
>
>
>
> Thanks
>
>
>
>
> Don Lowry, R.M.E.
>
> Vice President
> Dickerson Fire Protection, Inc.
> (254) 662-3777 office
> (254) 379-1442 Cell
> www.dickersonfire.com
>
> P Be Responsible! Print this email only when necessary.
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to