There are several systems which are UL listed for use on fire protection 
systems.  Some have limitations so you need to read their specs to determine 
applicability.

http://database.ul.com/cgi-bin/XYV/cgifind.new/LISEXT/1FRAME/srchres.html?collection=/data3/verity_collections/lisext&vdkhome=/data3/verity_sw_rev24/common&SORT_BY=textlines:asc,ccnshorttitle:asc&query=VGNJ%3CIN%3ECCN+and+not+GUIDEINFO
 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tom Wellen
Sent: Tuesday, March 24, 2009 11:17 AM
To: [email protected]
Subject: Re: Not Insulating Branchlines

Don,

The heat tracing for branch lines have to listed.  The heat tracing is not 
listed yet.  We did a Technical Update last August on this subject.  See below 
3rd paragraph.

Tom Wellen - AFSA



We have a building with an unheated attic space of approximately 3,900 square 
feet. The project specifications are requiring a wet fire protection system 
with the piping to be insulated and heat traced to prevent freezing. Is it the 
intent of Section 8.16.4.1 to allow this method of freeze protection for an 
entire system in lieu of a dry type system? Would sprinkler heads be protected 
from freezing by heat tracing branch line piping?"

We have reviewed the 2007 edition of NFPA 13 as the applicable standard. Our 
informal interpretation is that heat tracing is permitted in lieu of a dry pipe 
system but heat trace products are not yet available for branch line 
applications.

A manufacturer has reported that there is no heat tracing cable available with 
a listing for branch lines since the testing procedures have not yet been 
developed or defined by FM or UL. UL has been contacted and they confirmed that 
there is not yet a test standard and that a significant amount of work must be 
completed on the ANSI standard before testing can begin. A time estimated 
completion date has not yet been identified.

The heat tracing will affect the sprinklers thus the testing standard will have 
to address this issue. The concern is that the tracing wire may overheat the 
branch line and activate the sprinkler. The current UL listing is for use on 
piping between the system control valve and the system branch lines, but does 
not include the branch lines. Thus a dry pipe or antifreeze system should be 
installed for attic space unless the space is heated above 40 degrees F where a 
wet pipe system could be installed.




On Mar 24, 2009, at 10:35 AM, Don Lowry wrote:

> What is the main reason we cannot insulate and heat strip Branch 
> lines,  I have always pointed out to every owner, AHJ and engineer 
> that it is "unacceptable practice" per standard, however several 
> authorities here in Texas have been allowing and encouraging this 
> practice.  I need to give them a good reason other than the standard 
> says so.  The handbook doesn't quite explain this.
>
>
>
> Thanks
>
>
>
>
> Don Lowry, R.M.E.
>
> Vice President
> Dickerson Fire Protection, Inc.
> (254) 662-3777 office
> (254) 379-1442 Cell
> www.dickersonfire.com
>
> P Be Responsible! Print this email only when necessary.
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to