It is my understaning that you are supposed to flow enough water to get a
minimum drop of 10% in the static pressure.  If a single 2?" outlet doesn't
do it, you may need to open a 2nd, or the 4" connection.  Be sure to do the
proper modifications to the formula if you use the pumper connection. 