2002 NFPA-291- 4.3.6 John Drucker Fire Protection Subcode Official
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Tuesday, March 24, 2009 3:41 PM To: [email protected] Subject: RE: Flow Test It is my understaning that you are supposed to flow enough water to get a minimum drop of 10% in the static pressure. If a single 2?" outlet doesn't do it, you may need to open a 2nd, or the 4" connection. Be sure to do the proper modifications to the formula if you use the pumper connection. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Nick Melosi Sent: Tuesday, March 24, 2009 12:39 PM To: [email protected] Subject: Flow Test Is there any reason to flow (2) 2-1/2" outlets for a flow test? Both outlets are being flowed at the same time, on the same hydrant. -- Nick Melosi 813.944.2008 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ NOD32 3958 (20090324) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)