Help me understand. If 1 stairwell is "up", with aturnstyle at the bottom and 
doors that dont have handles on the outside, how will they be used for egress? 
And they would not be reqd exits if only 2 means of egress are reqd per floor.

The ahj wanted a hose valve in a cabinet outside the stairwell. The subject is 
still out for debate....

Sent from my Windows MobileĀ® phone.

-----Original Message-----
From: [email protected] <[email protected]>
Sent: Wednesday, March 25, 2009 7:59 PM
To: [email protected] <[email protected]>
Subject: Re: side by side standpipes

If nobody is using it, who is leaving and entering? In a highrise, I agree, but 
in an open atria building, it doesn't make sense. Everyone, including first 
responders (at least initially) are going to be entering and exiting through 
the public areas. Is the enclosed stairway any more than a receptacle for the 
standpipe on that situation?

Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Steve Leyton" <[email protected]>

Date: Wed, 25 Mar 2009 17:42:24 
To: <[email protected]>
Subject: RE: side by side standpipes


It does NOT matter what guests and occupants do whilst egressing; the
stairs are required to be protected for the safety of those leaving and
also those entering a building, i.e. responders.   That's why designers
can have all the escalators and convenience stairs they want, but still
have to provide a code-prescribed complement of exit stairs that are
protected by fire-resistive construction.  And furthermore, why we place
standpipe equipment within those protected enclosures.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Wednesday, March 25, 2009 5:39 PM
To: [email protected]
Subject: RE: side by side standpipes

However, they are going to be used as primary egress by patrons of 
the mall because that is the exit they are familiar with. Most 
enclosed stairways in this type of building are sufficiently well 
hidden so they will not be used because they can't be found. Not 
counting escalators (and fixed stairs in the mall area) for egress 
makes no sense. Also, when the FD responds to a fire, are they going 
for the stair towers or the main mall space? (Same could be said for 
buildings with large open atria, such as CNN Center.)

BTW, who makes the decision which stairways are required and which 
are "convenience"? How do you choose?



At 08:04 PM 3/25/2009, you wrote:
>Nope.  Escalators are a convenience appliance so no standpipes required
>at escalator landings.  They don't count for squat in the egress plan
>and are pretty much always open ...
>
>Steve Leyton
>Protection Design & Consulting
>San Diego, CA
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd
>Williams
>Sent: Wednesday, March 25, 2009 4:36 PM
>To: [email protected]
>Subject: Re: side by side standpipes
>
>So if you have a 4-story mall with escalators, you have to put a
>standpipe on each of these as well?
>
>At 07:07 PM 3/25/2009, you wrote:
> >ignoring convenient stairs as already addressed, it I certainly would
> >not be the one ATTEMPTING to argue just because the design added more
> >exits than minimally required I can leave out standpipes just because
> >of such loose wording.  IF you provide extra exits they all are
> >treated as full fledge exits and get all the bells and whistles of
the
> >other exits.  There is room to dance but I suggest to my members to
> >keep their butts in the chairs until a better song starts.
> >
> >Roland
> >
> >On Mar 25, 2009, at 3:36 PM, Chris Cahill wrote:
> >
> > > Dude, the standard is clear in every required exit stair.  Even
the
> > > IFC uses
> > > similar language.  If it ain't required you don't need a
standpipe.
> > > As a FF
> > > I of course think that would be bad design as I would have no idea
> > > when the
> > > building is on fire which stairs are required and which aren't.
> > > Thus I
> > > wouldn't know where to find standpipes.  As an FPE I agree with
> > > myself the
> > > FF.  Further I'd walk from a job (in a normal economy) where the
> > > standpipes
> > > weren't in every stair leading to an egress.  In this economy I'd
> > > certainly
> > > write lotsa CYA letters for the only job we would have.  (Sorry I
do
> > > need to
> > > eat).  As a former AHJ I'd fight for every stair until the judge
> > > overruled.
> > > My only case lost as AHJ was over an exterior standpipe for a
> > > Cathedral
> > > copper reroofing job where the Chief wanted a standpipe to reach
the
> > > top
> > > (over 250' above grade no access from the inside).  Tactically the
> > > Chief was
> > > right but the City Council sided with God's representative.  Once
>that
> > > happened the City couldn't proceed to a judge.  I assume I'm going
> > > to Hell
> > > anyway so arguing against God really didn't chance anything.
> > >
> > > Now I can't think of a place where a stair was there but not
> > > required, but
> > > it is certainly theoretically possible.  (Assuming something can
be
> > > "certainly theoretical")  Closest comes to mind is a convenience
>stair
> > > connecting several floors.  Some might go to street some might
not.
> > >
> > > In a legal contest the required part is going to be key if all the
> > > experts
> > > like the architect show up and have all the exiting calc's done
> > > showing the
> > > stair in question is not required. My money is on the NFPA
committee
> > > believes all stairs get standpipes but that is not what they wrote
-
> > > Steve.....
> > >
> > >
> > > In a legal deposition (or worse on cross in front of the judge) on
> > > the side
> > > of the standpipe how are you going to answer the questions along
the
> > > line of
> > >
> > >
> > > Mr. Huggins have you reviewed the Architects exiting analysis?
> > >
> > > Assuming you had the follow up is -
> > >
> > > Mr. Huggins is there anything wrong with the analysis as it
applies
> > > to the
> > > minimum requirements of the Code?
> > >
> > > Assuming there wasn't -
> > >
> > > Mr. Huggins does the analysis show the stair in question is
>required?
> > >
> > > And you wouldn't have gotten this far if it was required -
> > >
> > > Does the IFC and NFPA 14 refer to standpipes in required stairs?
> > >
> > > You really are in a corner to say yes -
> > >
> > > And finally Mr. Huggins what does the LAW say about non-required
> > > stairs?
> > >
> > > I'd guess you'd respond "nothing, but...."
> > >
> > > And your counsel will have no choice but to drop the matter.
> > >
> > > I try to use my powers for good so let's change the IFC and NFPA
14
>to
> > > change this loop hole. Might be as simple as dropping the word
> > > required.
> > >
> > > Now I don't know if Greg's stairs are required or not.  I tend to
> > > think they
> > > are required so really the discussion is mute but it does reveal a
> > > flaw in
> > > the code that until now I had not thought of.
> > >
> > > Chris Cahill, P.E.
> > > Fire Protection Engineer
> > > Sentry Fire Protection, Inc.
> > >
> > > 763-658-4483
> > > 763-658-4921 fax
> > >
> > > Email: [email protected]
> > >
> > > Mail: P.O. Box 69
> > >        Waverly, MN 55390
> > >
> > > Location: 4439 Hwy 12 SW
> > >              Waverly, MN 55390
> > >
> > > -----Original Message-----
> > > From: [email protected]
> > > [mailto:[email protected]] On Behalf Of
>Roland
> > > Huggins
> > > Sent: Wednesday, March 25, 2009 4:36 PM
> > > To: [email protected]
> > > Subject: Re: side by side standpipes
> > >
> > > Just because the design exceeds the minimum number of exits needed
>to
> > > meet the travel distance does NOT allow you to say the extra exit
is
> > > not REQUIRED so no standpipe in it.  If it is an actual stairway
>exit,
> > > it is considered required.
> > >
> > > Roland
> > >
> > > On Mar 25, 2009, at 9:46 AM, Greg McGahan wrote:
> > >
> > >> This is an unusual case - it is not for volume or congestion -
>there
> > >> are 4 stairs, (2 sets) within 50-60 feet of each other in an
> > >> amusement building. You pay to go up but you get to come down for
> > >> free.
> > >>
> > >> My thoughts were since the hose valves are serving the same area
it
> > >> is overkill to calc 1,000 gpm at an elevation of only 50' -
manual
> > >> wet should be allowed per law, but the EOR says auto is what he
> > >> wants, serving about 14,000 sqft per floor.
> > >>
> > >> But Ok, I got what I needed - thanks.
> > >>
> > >> Greg McGahan
> > >> Operations Manager
> > >>
> > >> Living Water Fire Protection
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > For Technical Assistance, send an email to:
>[email protected]
> > >
> > > To Unsubscribe, send an email
>to:[email protected]
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > For Technical Assistance, send an email to:
>[email protected]
> > >
> > > To Unsubscribe, send an email
>to:[email protected]
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to:
>[email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[email protected]
>
>To Unsubscribe, send an email
to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to