Just a follow up to our earlier discussion of "As Built" drawings. The NEW NFPA 3, Std for commissioning states the following:
3.3.5.1 Record (Plan) Drawing. A design, working or as built drawing that is submitted as the final record of documentation for the project. A drawing is also referred to as a plan. This wording allows the use of "Installation or submittal drawings" as "RECORD" drawings. As built requirements are confined to the bid documents, and not required by NFPA 3, but allowed to substitute for design or working drawings. If the EOR requires "AS Built" drawings, in the bid doc's then the cost of preparing them should be in the bid price. If this is not what you think should be happening, submit a proposal for any changes you want to NFPA 3 before the closing date. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)