Sorry for the delay in responding to this thread but it's been one of those 14 day weeks ..
Just wanted to add some support to the exterior deck protection discussion and also add to the top floor - nothing above so why put a head there idea .... The link below is a final Committee Interpretation issued by the ICC Fire Code Committee on this topic of 13-R and exterior deck protection and they also weighed in on the thought of nothing above .. and indicate that the top floor head over an exterior balcony REQUIRES protection. I point that the section requires exterior balconies and decks to have protection and does not provide for any exception to top floor or uncovered balconies. Just adding my fuel to the fire as it were .. http://www2.iccsafe.org/cs/committeeArea/pdf_file/FI_03_32_06.pdf Dave P. An AHJ in NJ & Member IFC Interp. Committee _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)