Sorry for the delay in responding to this thread but it's been one of those
14 day weeks ..

 

Just wanted to add some support to the exterior deck protection discussion
and also add to the top floor - nothing above so why put a head there idea
....

 

The link below is a final Committee Interpretation issued by the ICC Fire
Code Committee on this topic of 13-R and exterior deck protection and they
also  weighed in on the thought of nothing above .. and indicate that the
top floor head over an exterior balcony REQUIRES protection.  I point that
the section requires exterior balconies and decks to have protection and
does not provide for any exception to top floor or uncovered balconies.

 

Just adding my fuel to the fire as it were .. 

 

http://www2.iccsafe.org/cs/committeeArea/pdf_file/FI_03_32_06.pdf

 

Dave P.

An AHJ in NJ & Member IFC Interp. Committee

 