I've done a few of the partial systems according to NFPA 101, but as 
you say, it is just a couple of heads in a space. That tops out a 6 
sprinklers. However, the IBC one appears to go to 20. The one I have 
been asked to look at is 18.



At 08:32 AM 3/31/2009, you wrote:
>I have done a few of these type systems. Usually the ones I have done
>involve a mechanical room with a gas furnace or an elevator equipment room.
>
>Karen Purvis
>Senior Designer
>Facility Systems Consultants
>713 South Central Street,
>Suite 101
>Knoxville, TN 37902
>ph.865-246-0164
>fax 865-246-1084
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Tuesday, March 31, 2009 7:44 AM
>To: [email protected]
>Subject: Limited Area sprinkler systems
>
>The IBC mentions Limited Area sprinkler systems with a veiled
>reference being 20 sprinklers or less. However, there is no formal
>definition or description as to what they are or where they are
>allowed. Any thoughts or experience with this? I have a proposal on
>my desk for a partial system covering some sleeping rooms above a
>restaurant (for employees). The rest of the building is unprotected.
>Supposedly it is being required to renew their liquor permit. Since I
>doubt the Liquor Commission has jurisdiction over fire protection,
>I'm assuming that this is coming from the Fire Marshal.
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to