Ok, I understand better what you are doing.   

Check this site, they have some sizing and selection calculators.

http://www.controlvalves.com/valvemaster/default.aspx
 
Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Friday, April 03, 2009 9:16 AM
To: [email protected]
Subject: RE: Fill line for suction tank

Craig,

The fill line is fed from the 10" loop charged by the existing electric 
pump/jockey pump. 

We plan on re-circulating the water back to the tank, connecting the 8"
meter discharge directly to the tank (increasing the connection point on the 
tank and interior tank piping of the fill line to 8")and connecting the supply 
for the fill, with ACV behind it.

The main question I had was the sizing of the ACV and fill line from the UG to 
the connection of the tank. Through info from ACV manufacturers tech dept and 
comments from a fellow forumite I intend on using a 4" pressure sustaining ACV 
allowing only the jockey to come on.

Any other comments are definitely welcome.

Thank You,

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, April 03, 2009 7:51 AM
To: [email protected]
Subject: RE: Fill line for suction tank

Bobby, 

Do you know what kind of flow you get through the fire main from the city water 
supply?  You need to know if there's enough pressure to overcome the tank 
height and be able to fill the tank in the appropriate amount of time per NFPA 
22.

NFPA 20 gives you the option of discharging the flow meter output back into the 
suction side of the pump, there are however some issues and restriction on the 
installation.  One issue is that by creating this closed loop, you do not test 
the suction supply system piping, valves, etc.  

If possible it is often preferable to take the flow meter discharge back to the 
tank.  This is mentioned in A.5.19.2.1.1.

If you have NFPA 20, 2007 check out some of the information in A.5.19.1.1 - 2. 

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, April 02, 2009 9:25 AM
To: [email protected]
Subject: Fill line for suction tank

We are working on a project where the owner has an electric fire pump fed from 
the city water supply charging a 10" loop around the facility. At the back of 
the property they want a water storage tank with a diesel pump for back up. The 
insurance company is allowing the tank to be filled from the charged UG loop. I 
plan on installing a pressure sustaining alt. control valve and have the 
pressure set to allow the jockey to come on when the ACV opens but not the 
electric fire pump. How about sizing the ACV and fill line?. And does this 
scenario sound correct? They also want a metering device for the pump instead 
of a test header to recirculate the water back into the tank. We plan 
increasing the fill line to 8" (required size per NFPA for metering device of a 
2000gpm pump) and connecting the discharge piping from the metering device to 
the fill line between the tank and the discharge control valve of the ACV. Does 
this scenario sound correct?

 

Thank You,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to