To: [email protected]
Subject: RE: Fill line for suction tank

Ok, I understand better what you are doing.   

Check this site, they have some sizing and selection calculators.

http://www.controlvalves.com/valvemaster/default.aspx
 
Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Friday, April 03, 2009 9:16 AM
To: [email protected]
Subject: RE: Fill line for suction tank

Craig,

The fill line is fed from the 10" loop charged by the existing electric
pump/jockey pump. 

We plan on re-circulating the water back to the tank, connecting the 8"
meter discharge directly to the tank (increasing the connection point on the
tank and interior tank piping of the fill line to 8")and connecting the
supply for the fill, with ACV behind it.

The main question I had was the sizing of the ACV and fill line from the UG
to the connection of the tank. Through info from ACV manufacturers tech dept
and comments from a fellow forumite I intend on using a 4" pressure
sustaining ACV allowing only the jockey to come on.

Any other comments are definitely welcome.

Thank You,

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, April 03, 2009 7:51 AM
To: [email protected]
Subject: RE: Fill line for suction tank

Bobby, 

Do you know what kind of flow you get through the fire main from the city
water supply?  You need to know if there's enough pressure to overcome the
tank height and be able to fill the tank in the appropriate amount of time
per NFPA 22.

NFPA 20 gives you the option of discharging the flow meter output back into
the suction side of the pump, there are however some issues and restriction
on the installation.  One issue is that by creating this closed loop, you do
not test the suction supply system piping, valves, etc.  

If possible it is often preferable to take the flow meter discharge back to
the tank.  This is mentioned in A.5.19.2.1.1.

If you have NFPA 20, 2007 check out some of the information in A.5.19.1.1 -
2. 

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, April 02, 2009 9:25 AM
To: [email protected]
Subject: Fill line for suction tank

We are working on a project where the owner has an electric fire pump fed
from the city water supply charging a 10" loop around the facility. At the
back of the property they want a water storage tank with a diesel pump for
back up. The insurance company is allowing the tank to be filled from the
charged UG loop. I plan on installing a pressure sustaining alt. control
valve and have the pressure set to allow the jockey to come on when the ACV
opens but not the electric fire pump. How about sizing the ACV and fill
line?. And does this scenario sound correct? They also want a metering
device for the pump instead of a test header to recirculate the water back
into the tank. We plan increasing the fill line to 8" (required size per
NFPA for metering device of a 2000gpm pump) and connecting the discharge
piping from the metering device to the fill line between the tank and the
discharge control valve of the ACV. Does this scenario sound correct?

 

Thank You,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to