FYI - In a similar situation with FM they say you "should" install all galv. pipe on a dry system. I had to talk and talk to get the "should" allowed and them to pass the black on the inside of the last one I did for one of their clients.
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Loren Johnson Sent: Monday, April 06, 2009 6:40 PM To: [email protected] Subject: RE: Factory Mutual: Remote Inspectors Test on wet system I have had numerous instances where FM and I went around and around on this issue. Even though it is permissable by NFPA 13, FM does not want the test station at the riser. I have had plan review letters and final field system acceptances by the engineers indicating the test station is to be moved to the most remote branch line. Regarding 2-8N, I have learned that this data sheet is no longer avail- able on the FM web site. It has been removed and is to be replaced by a complete new document: DS 2-0. This will be FM's own sprinkler system installation guide, which means they will no longer be referencing the "N" (for NFPA), where they had to pay a fee for use of the NFPA 13 document. The new document should be out later this year. Loren Johnson - CFPS, CET The Hitchcock Company Peoria, IL --- On Mon, 4/6/09, Reed Roisum <[email protected]> wrote: > From: Reed Roisum <[email protected]> > Subject: RE: Factory Mutual: Remote Inspectors Test on wet system > To: "'[email protected]'" <[email protected]> > Date: Monday, April 6, 2009, 6:09 PM > FM seems to prefer the test > connection to be at the remote branch line, but it is a > should not shall. > Check out Data Sheet 2-8n A-4-15.4.2. > > Reed A. Roisum, CET > Fire Protection Technician > > Ulteig Engineers, Inc. > 3350 38th Avenue South > Fargo, ND 58104-7079 > > Direct Number: 701.280.8580 > Mobile: 701.212.8810 > Main Office: 701.280.8500 > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] > On Behalf Of [email protected] > Sent: Monday, April 06, 2009 5:59 PM > To: [email protected] > Subject: Re: Factory Mutual: Remote Inspectors Test on wet > system > > Does anyone know if FM Global requires inspectors test to > be remote endĀ of > wet system? > Or do they allow it at riser? > I know this issue of corrosion was discussed earlier and I > would likeĀ to > know what FM Global's position is on it. > > Forest Wilson > Cherokee Fire > **************A Good Credit Score is 700 or Above. See > yours in just 2 easy > steps! > (http://pr.atwola.com/promoclk/100126575x1221621488x1201450096/aol?redir=htt p:%2F%2Fwww.freecreditreport.com%2Fpm%2Fdefault.aspx%3Fsc%3D668072%26hmpgID > %3D62%26bcd%3DAprilfooterNO62) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)