NFPA 13 requires that all hangers be ferrous (contains iron, the 
primary component of steel), unless specifically approved. I do not 
know of a non-metallic hanger rod. Stainless would be the best 
option. You might be able to use regular plated rod if you coated it 
with spray galvanize in place, but I would have to do more research. 
BTW, how are the sprinklers? Are they coated?



At 09:42 AM 4/13/2009, you wrote:
>Non-Corrosive Hangers?  Does any one know of an accepted and/or 
>approved method of hanging
>(re-hanging) fire sprinkler pipe.  I am working with a customer to 
>replace all parking garage
>sprinkler pipe hangers.  The property is at the beach.  The salty 
>humid air has caused all of the
>existing painted (zinc plated) all-thread hanger rods to corrode.  I 
>have suggested stainless. The
>customer asked if there is some type of non-metal rod. If any one 
>has any information or methods of
>accomplishing a long lasting hanger assembly you input would be appreciated.
>
>
>
>Thank You,
>
>Mark E. Eckard S.E.T.
>Office: 239-693-8722
>Fax: 239-693-8792
>Cell: 828-851-0080
>[email protected]
>
>
>
>
>
>This e-mail transmission contains information that is intended to be 
>confidential and privileged.  If you receive this e-mail and you are 
>not a named addressee you are hereby notified that you are not 
>authorized to read, print, retain, copy or disseminate this 
>communication without the consent of the sender and that doing so is 
>prohibited and may be unlawful.  Please reply to the message 
>immediately by informing the sender that the message was 
>misdirected.  After replying, please delete and otherwise erase it 
>and any attachments from your computer system.  Your assistance in 
>correcting this error is appreciated.
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to