Agreed. Where I am located geographically, the low temps are temporary. Not
of a duration that a good insulation can't handle. I'm in a position to
answer a GC's question. But back to my question; can I or can't I use
insulation on branch lines (per NFPA13)? I'm against it. In my location the
problem I see with just insulation without heat tape is the water in the
part of the sprinkler just beneath the seat (I'm dealing with upright
sprinklers here). I would be very afraid of this. Plus the thickness of the
insulation may go to the diameter that may require sprigs.


Thanks to you and to Timothy for your input.

Russell



<Insulation on a pipe with non-flowing water is pointless (except for
temporary exposures to low temperatures).  Insulation can only slow the
transmission of heat from the pipe, it does nothing to produce heat.>  