NFPA #30 1.1.2 Thiscode shall not apply to the following.
(8) Storage, handling and use of fuel oil tanks anc containers connected
with oil-burning equipment.

Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Friday, April 24, 2009 10:04 PM
To: [email protected]
Subject: RE: Diesel Fuel Tank Emergency Vent

Ron, sorry I'm a bit late on this.   

NFPA 30 section 27.8.1 and A.27.8.1.6 may be helpful.  27.8.1 implies
vents
need to be piped outside, though it doesn't specifically say it.

Ed Kramer
Littleton, CO

 
> Our local AHJ is requiring that we pipe the emergency vents of a 150
> gallon UL 142 fuel tank outside. I have two questions.
> 
> Are the vents required by code or standard to be piped outside?
> 
> If we pipe them outside how do we calculate the added pipe and
fittings
> to be sure the vent will still operate properly?
> 
> Thanks for your help.
> 
> Ron Fletcher
> Aero Automatic Sprinkler
> Phoenix, AZ 85024

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to