Ron, it may not help your situation, but the NFPA 20 ROP and ROC contain
proposed revisions that would provide guidance on tank design.

Ed Kramer
Littleton, CO

 
> Class II combustible.
> 
> Ron Fletcher
> Aero Automatic Sprinkler
> 21605 N. Central Ave
> Phoenix, AZ 85024
> P: 623.580.7836
> F: 623.434.3420
> C: 602.763.4160
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ed Kramer
> Sent: Monday, April 27, 2009 8:25 AM
> To: [email protected]
> Subject: RE: Diesel Fuel Tank Emergency Vent
> 
> Ron, good catch.  Is diesel fuel considered 'oil'?  I didn't find any
> obvious definition (in 30 or 31).
> 
> Ed Kramer
> Littleton, CO
> 
> 
> 
> > NFPA #30 1.1.2 Thiscode shall not apply to the following.
> > (8) Storage, handling and use of fuel oil tanks anc containers
> connected
> > with oil-burning equipment.
> >
> > Ron Fletcher
> > Aero Automatic Sprinkler
> > 21605 N. Central Ave
> > Phoenix, AZ 85024
> > P: 623.580.7836
> > F: 623.434.3420
> > C: 602.763.4160
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Ed
> Kramer
> > Sent: Friday, April 24, 2009 10:04 PM
> > To: [email protected]
> > Subject: RE: Diesel Fuel Tank Emergency Vent
> >
> > Ron, sorry I'm a bit late on this.
> >
> > NFPA 30 section 27.8.1 and A.27.8.1.6 may be helpful.  27.8.1 implies
> > vents
> > need to be piped outside, though it doesn't specifically say it.
> >
> > Ed Kramer
> > Littleton, CO
> >
> >
> > > Our local AHJ is requiring that we pipe the emergency vents of a 150
> > > gallon UL 142 fuel tank outside. I have two questions.
> > >
> > > Are the vents required by code or standard to be piped outside?
> > >
> > > If we pipe them outside how do we calculate the added pipe and
> > fittings
> > > to be sure the vent will still operate properly?
> > >
> > > Thanks for your help.
> > >
> > > Ron Fletcher
> > > Aero Automatic Sprinkler
> > > Phoenix, AZ 85024
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to