I believe CPVC is considered a combustible penetration when running through a rated assembly and therefore would require a listed firestop assembly. Metal escutcheons provide no rating; the IBC permits only an escutcheon to cover the annular space of a sprinkler penetration when the pipe is noncombustible, i.e., steel, copper, conduit, etc.
Regards, Salvatore Izzo, P.E. SFPE Manager - Reliable Technical Services ________________________________________ From: [email protected] [[email protected]] On Behalf Of Bobby Gillett [[email protected]] Sent: Tuesday, April 28, 2009 10:56 AM To: [email protected] Subject: Rating of the sprinkler escutcheon Our situations - we have a hotel designed to 13R that requires our cpvc piping to be run through a fire rated wall between two units with 4.0K residential semi-recessed sidewall heads spraying into both units. The other is the extended coverage 8.0K semi-recessed sprinkler spraying into the stairwell (also fed by cpvc from the corridor). The question being asked by the fire marshall - What is the fire rating of the escutcheons? Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)