I believe CPVC is considered a combustible penetration when running through a 
rated assembly and therefore would require a listed firestop assembly.  Metal 
escutcheons provide no rating; the IBC permits only an escutcheon to cover the 
annular space of a sprinkler penetration when the pipe is noncombustible, i.e., 
steel, copper, conduit, etc.

Regards,

Salvatore Izzo, P.E. SFPE
Manager - Reliable Technical Services

________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Bobby Gillett 
[[email protected]]
Sent: Tuesday, April 28, 2009 10:56 AM
To: [email protected]
Subject: Rating of the sprinkler escutcheon

Our situations - we have a hotel designed to 13R that requires our cpvc
piping to be run through a fire rated wall between two units with 4.0K
residential semi-recessed sidewall heads spraying into both units. The other
is the extended coverage 8.0K semi-recessed sprinkler spraying into the
stairwell (also fed by cpvc from the corridor). The question being asked by
the fire marshall - What is the fire rating of the escutcheons?



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]







_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to