What about the sprinkler itself? Doesn't it offer something of value at the 
point of penetration?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sal Izzo (TECH- 
103)
Sent: Tuesday, April 28, 2009 9:59 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

I believe CPVC is considered a combustible penetration when running through a 
rated assembly and therefore would require a listed firestop assembly.  Metal 
escutcheons provide no rating; the IBC permits only an escutcheon to cover the 
annular space of a sprinkler penetration when the pipe is noncombustible, i.e., 
steel, copper, conduit, etc.

Regards,

Salvatore Izzo, P.E. SFPE
Manager - Reliable Technical Services

________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Bobby Gillett 
[[email protected]]
Sent: Tuesday, April 28, 2009 10:56 AM
To: [email protected]
Subject: Rating of the sprinkler escutcheon

Our situations - we have a hotel designed to 13R that requires our cpvc
piping to be run through a fire rated wall between two units with 4.0K
residential semi-recessed sidewall heads spraying into both units. The other
is the extended coverage 8.0K semi-recessed sprinkler spraying into the
stairwell (also fed by cpvc from the corridor). The question being asked by
the fire marshall - What is the fire rating of the escutcheons?



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]







_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to