that would be 1-hour FRR if building separation were 3 ft(half of 6 ft)
 between U occupancies.

reference:
  2006 IBC Table 602.
  Special mention at Section 406.1.2 and 406.1.3 for garages,
     but only as analogy.


1-hour FRR on each facing side might be enough to validate not
adding sprinklers.   of course, if there is not 1-hr FRR at this time
getting to that may be more cost than adding the sprinklers.

scot deal
excelsior fire

>
> You are familiar with the imaginary lot line concept in IBC 704.3?