Bob, I'd say that because the 'exception" is so specific (2 1/2 in starter pieces less than 12' long) that the intent was also specific and, in addition, because they used starter pieces as a criteria they mean only for branch lines. I think the handbook commentary for 9.3.5.3.3 suggests that it is a gimme for this single set of conditions.
On Wed, May 6, 2009 at 2:02 PM, Bob Knight <[email protected]> wrote: > NFPA 13 9.3.5.3.3 States, "The requirements of 9.3.5.3.1 shall not apply to > 2-1/2" starter pieces that do not exceed 12' in length". Is this section > limiting this to 2-1/2" piping or can it be assumed that starter pieces of > larger pipe sizes can also be included? > > Thank you, > > Bob Knight, CET > (208) 318-3057 > [email protected] > www.firebyknight.com > > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)