>From my understanding it is not the role of the fire sprinkler inspector to 
 do this.
He should maintain and inspect the heads for visual signs of corrossion,  
etc but the system should be maintained as installed and approved at time of  
installation.
The Inspector is not an engineer.
And the owner should tell the inspector if occupancy has changed. Then if  
temp ratings need looked at due to change of occupancy it should be 
forwarded to  a qualified engineer for review.
 
Forest  Wilson

Project Manager
Cherokee Fire Protection Co.
3195  Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx:  614-455-4324
cell: 937-307-5647


Tuesday, April 21 is Holocaust Remembrance Day.  May we never forget.


Visit our blog: _www.cherokee-fire.blogspot.com_ 
(http://www.cherokee-fire.blogspot.com/)  


FIRE SPRINKLERS SAVE LIVES!!



NOTICE: The information contained in this  email is intended to be solely 
for the use of the named individual or entity to  which it is directed and 
may contain information that is privileged or otherwise  confidential. It is 
not intended for transmission to, or receipt by, anyone  other than the named 
addressee (or a person authorized to deliver it to the  named addressee). 
It should not be copied or forwarded to any unauthorized  persons. If you 
have received this electronic mail transmission in error, please  delete it 
from your system without copying or forwarding it, and notify the  sender of 
the error by reply email or by calling Cherokee Fire Protection Co. at  
888-347-3079 toll free. 

 
In a message dated 5/8/2009 8:59:17 A.M. Eastern Daylight Time,  
[email protected] writes:

Is it  the intent of code to be able to identify the temperature rating
of a  sprinkler and therefore ensure that the proper rated(temperature)
sprinkler  is installed...from the annual inspection while walking the
floor?   

In other words, NFPA 13:6.2.5.1 states: Automatic sprinklers shall  have
their frame arms, deflector, coating material, or liquid bulb colored  in
accordance with the requirements of Table 6.2.5.1 or the requirements  of
6.2.5.2, 6.2.5.3, 6.2.5.4, or 6.2.5.5.

NFPA 25:2.1.1 states:  Sprinklers shall be inspected from the floor level
annually.

How  else is an owner/inspector supposed to keep track of properly  rated
sprinklers?

I understand there are exceptions for identifying  corrosion-resistant
sprinklers and ornamental sprinklers, but not for the  standard, everyday
use upright...


Duane Johnson, PE
Program  Manager
Division of the Fire Marshal (Support Contractor)
Office of  Research Services
National Institute of  Health

_______________________________________________
Sprinklerforum  mailing  list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For  Technical Assistance, send an email to:  [email protected]

To Unsubscribe, send an email  to:[email protected]
(Put the word unsubscribe in  the subject field)


**************A Good Credit Score is 700 or Above. See yours in just 2 easy 
steps! 
(http://pr.atwola.com/promoclk/100126575x1221322931x1201367171/aol?redir=http://www.freecreditreport.com/pm/default.aspx?sc=668072&hmpgID=115&bcd
=May5509AvgfooterNO115)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to