Tell the GC and or contractor to figure it out themselves. You don't want the 
aggrivation or liability of doing any more than review.


------Original Message------
From: å... ....
Sender: [email protected]
To: [email protected]
ReplyTo: [email protected]
Sent: May 8, 2009 1:10 PM
Subject: review of sprinkler plans ends up with GC requesting the reviewer to 
provide additional plan sheet because contractor don´t want to

Am reviewing a drawing set for a medical
outpatient facility where sprinkler
contractor is doing a retrofit:   changing out armovers
and over 200 sprinkler heads

I asked the sprinkler contractor to

A.  provide a sheet with information that included
enough of the site underground to:
   tell if the UG  was fed by a loop or dead end,
   location and dimension of underground pipe
   location and specs on FDC and BFP,
   where the gauge and flow hydrants were
   elevation of the same and finished floor
   include the new waterflow test
   derate the HC coefficient for existing mains that are to
      remain in place


B. and the sprinkler contractor was asked to brace the existing
mains per 2007 NFPA 13.

sprinkler contractor refuses to do the above, and GC
  wants me to draw up the site plan showing UG, because
  this internationally recognized sprinkler company, simply
  will take too long and the GC wants the job done.

Sprinkler contractor is probably saying it is not in their
  bid and scope of work, but I don´t see where in NFPA
  13, that it is NOT in their scope of work.  Am I
  wrong, dead wrong, or kinda wrong.

scot deal
excelsior fire
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


Sent from my Verizon Wireless BlackBerry
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to