Ken,

I think you are on target. You are making your best recommendation as 
an FPE, which is appropriate. It's almost your duty as an advisor to 
the client. Remember, the Code only tells you what is required, but 
what is best might often be beyond that. However, if that is all the 
owner wants to do and it is not required by Code, you should yield to 
his request (in this situation).

Todd


At 08:17 AM 5/12/2009, you wrote:
>Chiller plant determined by architect to be F-2 occupancy:  No sprinkler
>protection required under current code.
>
>However, owner wants to bid alternate for sprinklers in main chiller room,
>but no sprinklers in adjacent electrical equipment room.  Electrical
>equipment room has only dry equipment, transformers of 75 kVA, but no rated
>separation from chiller room.
>
>I am pressing for sprinklers in electric equipment room, or 2-hour
>separation with the alternate to provide sprinklers for the chiller room.
>Would members say I am being overly conservative and best to be just be
>content if owner wants to add some sprinkler protection?  I see the
>unprotected electrical area as reducing the value/advantage of sprinklers in
>the chiller room.
>
>Ken A. Nisly-Nagele, P.E.
>Mechanical Project Engineer
>
>Applied Engineering Services, Inc.
>9100 Keystone Crossing, Ste 200
>Indianapolis, IN 46240
>Voice:  317.810.4141
>Fax:  317.810.4140
>www.applied-e-s.com <http://www.applied-e-s.com/>
>
>   <file:///G:/Group/Marketing/Logo%20small.jpg>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to