Here's a more mundane example:
Bar/restaurant in rural mountaintop location, wildly successful for years.
Burns down.
Rebuilt, kitchen equipment is delivered, and 2 weeks before re-opening,
burns down again. Slamander.
Rebuilt with sprinklers last year.
Business booming again, and Owner has a lot more confidence history won't
repeat itself.

Owner wryly observed halfway thru the sprinklered rebuild that it was very
easy for him to project revenue- it was continuing to be zero. He's now got
partners, and some additional debt, but its up and serving customers again.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, May 12, 2009 9:09 AM
To: [email protected]
Subject: RE: Value of additional Sprinkler Coverage

A project we completed last year had a similar situation.  The owner didn't
want to spend the money to protect the electrical equipment.  Underwriter
recommended it but owner was very determined to have things their way.
Their construction mgr. mentioned about another project he had been on with
an unprotected electrical installation and that the site did have a fire.
When asked about down time he said they were off-line for almost 8 months.
When we asked the owner if he had considered down-time and time to rebuild,
he said they probably could not return to 100% operational status in that
length of time.  As he considered what was presented he opted to go with the
full protection.

It's not about arm twisting or trying to get our way, it's about giving an
owner the information he needs to make a rational and fact based decision
not one based on fantasy, fear and myths.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, May 12, 2009 9:02 AM
To: [email protected]
Subject: RE: Value of additional Sprinkler Coverage

Business Interruption isn't addressed by code. Sure is important, and a
small investment in sprinkler can avoid millions in
shutdown/replacement/loss of revenue/loss of customers going elsewhere.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, May 12, 2009 8:55 AM
To: [email protected]
Subject: RE: Value of additional Sprinkler Coverage

This is a common issue in industrial facilities.  Apparently he sees value
in protecting his chillers against fire.  Does he feel that his electrical
equipment is expendable?  If the whole
"water-on-electrical-equipment=electrocution or damage" issue is his driver
for omitting sprinkler protection from the electrical room, remind him that
any fire within this area will be dealt with by use of water.  Without
sprinklers it will be firemen with hoses delivering large amounts of water.
Plus by that time, his electrical gear will be a total loss from the heat
and fire.  Can he afford to interrupt his operation long enough to replace
the equipment, wiring, conduit, controls and possibly the building?  Most
will say no, they couldn't afford that kind of interruption, and especially
not in today's economy.  If he has fear of the electrocution or water damage
issue, you can always do the pre-action thing to offer him some level of
comfort.  

Often these areas are considered low hazard areas and by code don't require
sprinkler protection.  However the driver that usually results in them being
protected is their importance to the operation of the facility.  These are
expensive items with long lead times for delivery.  Depending on their use,
their failure can result in failure of other equipment.  So that's why it's
good to ask the owner what level of importance these types of support areas
have to their overall operation.  

So no, you're not being overly conservative, you're trying to look out for
his best interest.  If he has an insurance underwriter have they been
involved or offered any opinion?  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ken
Nisly-Nagele
Sent: Tuesday, May 12, 2009 8:18 AM
To: [email protected]
Subject: Value of additional Sprinkler Coverage

Chiller plant determined by architect to be F-2 occupancy:  No sprinkler
protection required under current code.
 
However, owner wants to bid alternate for sprinklers in main chiller room,
but no sprinklers in adjacent electrical equipment room.  Electrical
equipment room has only dry equipment, transformers of 75 kVA, but no rated
separation from chiller room.
 
I am pressing for sprinklers in electric equipment room, or 2-hour
separation with the alternate to provide sprinklers for the chiller room.
Would members say I am being overly conservative and best to be just be
content if owner wants to add some sprinkler protection?  I see the
unprotected electrical area as reducing the value/advantage of sprinklers in
the chiller room.
 
Ken A. Nisly-Nagele, P.E.
Mechanical Project Engineer
 
Applied Engineering Services, Inc.
9100 Keystone Crossing, Ste 200
Indianapolis, IN 46240
Voice:  317.810.4141
Fax:  317.810.4140
www.applied-e-s.com <http://www.applied-e-s.com/> 
 
  <file:///G:/Group/Marketing/Logo%20small.jpg> 
 
_______________________________________________


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to