We have recently run into an EOR (sprinkler scientist) that specified
S40 galvanized with cut groove or thread for a bunch of pre-action
systems because of the water that will be trapped on the up hill side of
the roll groove bump. 

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, May 12, 2009 8:10 AM
To: [email protected]
Subject: RE: Galvanized pipe - threaded reducer tees vs. thread-o-lets

One excuse I got was from a specifying engineer who didn't know you
could groove schedule 40 pipe.  He assumed it had to be threaded.  He
didn't know about cut versus roll grooving. 

2" seems to be the standard break point for thread to groove.  I was
told by one that it was based on a military requirement and he thought
that if it was good for the government it should be good for all of his
projects.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Tuesday, May 12, 2009 11:02 AM
To: [email protected]
Subject: RE: Galvanized pipe - threaded reducer tees vs. thread-o-lets

Oh and how do you spray the inside of the pipe where the weld occurred?
This assumes the galv. is effected on the inside at the weld which may
not be true. 

Chris 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Tuesday, May 12, 2009 9:59 AM
To: [email protected]
Subject: RE: Galvanized pipe - threaded reducer tees vs. thread-o-lets

How exactly are you going to re-galv?  Is spray paint really
galvanization?

Always puzzled me why one (client/PE) would on smaller pipe insist on
cutting most of the materials off in the threading process over roll
grooving and preserving most of the wall thickness.  Seems to me
grooving with all things being equal would last longer than threading.  

Can any one shed light on OK to groove larger pipe but must thread
smaller?
2" seem to be the break point.  Applies to both galv and black, again
all
things being equal.    

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Davis,
Adam
Sent: Tuesday, May 12, 2009 9:20 AM
To: [email protected]
Subject: RE: Galvanized pipe - threaded reducer tees vs. thread-o-lets


The client has agreed to use grooved connection for the 6" main but not
for the 2".  It seems the practical solution is to use TOLs and
re-galvanize to save on field labor and cost.  I'm unfamiliar with
galvanized pipe so the forum's input has been helpful.  Thanks


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, May 12, 2009 10:09 AM
To: [email protected]
Subject: RE: Galvanized pipe - threaded reducer tees vs. thread-o-lets

Is there a requirement to use threaded versus grooved?  

If you have corrosion issues the "clamp fittings" aren't galvanized so
they could corrode so it's logical that you'd avoid them. 

If you are threading pipe, the field install labor would be less if you
have the thread-o-let in the main.  From a materials cost the TOL would
also come out cheaper, from all areas of installation the TOL would be
cheaper.  Sure the shop labor would be more for the TOL but that would
have to be greatly offset by the other savings in labor and materials.

Also I hope you don't intend to ask for 6" threaded pipe, 2" will get
enough frowns.




Craig L. Prahl

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Davis,
Adam
Sent: Tuesday, May 12, 2009 9:29 AM
To: [email protected]
Subject: Galvanized pipe - threaded reducer tees vs. thread-o-lets

I have a 6" galvanized main and have to come off with 40 2" branch
lines.
I'm trying to determine the least costly way to transition to the 2"
branch lines.  The two options I have are using 6"x2" threaded reducer
tee or 2"
thread-o-let and re-galvanizing the weld.  The client requires
galvanized pipe and does not want to use mechanical clamp fittings.  Any
suggestions to which method is the least expensive? 

 

Thanks

Adam Davis


NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any
viewing, copying or distribution of, or reliance on this message by
unintended recipients is strictly prohibited. If you have received this
message in error, please notify us immediately by replying to the
message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any
viewing, copying or distribution of, or reliance on this message by
unintended recipients is strictly prohibited. If you have received this
message in error, please notify us immediately by replying to the
message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to