Anybody got an MSDS  for this pipe? What exactly are these
"chemical components of the anti-microbial coating" and are they harmful to 
pipefitters?

BTW some of y'all might be interested in my new project. The new Fire 
Station #1 in
Downtown Orlando. It's a big one!

http://www.cityoforlando.net/fire/Firehouse1%20renderings.htm




----- Original Message ----- 
From: "Terri Leyton" <[email protected]>
To: <[email protected]>
Sent: Tuesday, May 12, 2009 5:10 PM
Subject: Tyco Update on Allied ABFII - Steel Coated Pipe and CPVC


> Tyco Update on Allied ABF(r)
> Steel Coated Pipe and CPVC
>
>
>
> The following notice has been issued by Tyco Fire Suppression & Building
> Products regarding CPVC compatibility.
>
> "Since its introduction in 2004, Allied Tube & Conduit's ABF(r) II
> anti-microbial steel sprinkler pipe has been installed and successfully
> maintained in millions of feet of steel-CPVC applications. Recently,
> Allied and Tyco Fire Suppression & Building Products became aware of a
> small number of sites with environmental stress cracking (ESC) failures
> of CPVC pipe and fittings. Some customers have expressed concern that
> the ESC was caused by chemical components of the anti-microbial coating
> on the ABF II coated steel pipe. To put this into context, these
> instances of failure involve less than one tenth of one percent of the
> installed base in combined systems in the Americas.
>
> ESC failures can occur in CPVC pipe and fittings when exposed to
> sufficient levels of stress and when an environmental stress cracking
> agent is present in sufficient concentration over a period of time. An
> ESC failure results in cracks in the wall of the pipe or fitting. These
> cracks typically result in weeping, dripping, and other small leaks from
> the fire sprinkler system.
>
> In response to recent concerns, Tyco gathered a team of scientists and
> industry experts working in conjunction with Lubrizol and customers to
> investigate. Tyco's investigation has included an analysis of how the
> ABF II coating may be released and transported through the piping
> system, and how it may interact with other components of the system.
>
> The initial findings of the investigation suggest that in some
> circumstances, components of the ABF II coating may wash from the
> interior of the steel pipe and transport to downstream CPVC pipe and
> fittings. In combination with ancillary products used in the system,
> such as cutting oils and lubricants, the ABF II coating components may
> collect in sufficient concentration and in some circumstances pose a
> potential risk to the CPVC.
>
> However, in the instances of CPVC failure investigated and not linked to
> poor quality CPVC pipe or fittings, unusually high mechanical stress has
> been present. Unusually high amounts of mechanical stress create an
> environment that makes CPVC pipe and fittings more susceptible to ESC.
> For example, some approved hangers have been found to put an excessive
> mechanical stress on the pipe. Tyco is continuing to analyze the causes
> and effects of mechanical stresses on the safety tolerances of CPVC pipe
> and fittings used in conjunction with ABF II coated steel pipe. Because
> steel-CPVC systems are installed using a variety of techniques and in a
> myriad of diverse environments, there are a large number of mechanical
> and chemical variables and combinations that a comprehensive
> investigation must include.
>
> It is important to note that Tyco's analysis to date does not indicate
> an inherent risk associated solely with using ABF II coated steel pipe
> in combination with CPVC pipe and fittings. As a conservative approach
> while the investigation continues, Tyco recommends that ABF II coated
> steel pipe not be used in new systems containing CPVC. For these
> applications, Allied will continue to make uncoated steel pipe
> available. ABF II coated steel pipe should still be used in all-steel
> systems, where it provides industry-leading anti-microbial protection.
>
> The overwhelming majority of installations of ABF II coated steel pipe
> with CPVC pipe and fittings have provided reliable service without
> incident for many years. Based on this experience and the initial
> findings, Tyco does not believe that previously installed systems are at
> an increased risk of ESC failure. For systems that are already installed
> or in the process of being installed, Tyco does not recommend removal of
> the CPVC or ABF II coated steel pipe.
>
> For additional information or questions, visit
> <http://rs6.net/tn.jsp?et=1102558568972&s=739&e=001lDIXBoYU8jcRfyYWud2CN
> gEnSp_lMORuxA0h4CyiqGRosqybbJzhhOVL3y0PeIhQVPZPiA_RtXXp-dMPTG-6TiiXnkESF
> lBWEG_ilCcvIMejJZI1KJoEpHikOpr6X8Hh6yvkC5qdw2Y=>
> www.alliedtube-sprinkler.com/cpvc or contact Tyco at 1-800-890-2278 in
> the US and 1-708-339-1610 ext. 7301 outside the US.
>
> As a responsible leader in the fire sprinkler industry, Tyco is
> committed to the industry and its customers. Tyco will continue its
> investigation, testing, and analysis to enable it to provide the
> additional answers that it, the industry, and its customers seek. Thank
> you for your continued support."
>
>
>
>
>
> Terri Simmons Leyton
>
> PROTECTION DESIGN & CONSULTING
>
> 8849-B Complex Drive
>
> San Diego, CA 92123
>
> -------------------------------------------------------------
>
> Ph:      858-751-2930 - ext. 101
>
> Fax:    858-751-2933
>
> Cell:  619-871-8450
>
> Children are the living messages we send to a time we will not see.
> --John W. Whitehead
>
> Fire Sprinklers Save Lives, Property and Firefighters!
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)


--------------------------------------------------------------------------------



Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com
Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date: 2/2/2009 
7:51 AM

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to