This is from the Viking model VK540 sprinkler.

Hydraulic Calculation Note: To determine the number of sprinklers to
calculate per branch line:
Determine sprinkler spacing. (Refer to the appropriate Installation
Standard and the Authority Having Jurisdiction.)
Determine size of the remote area by multiplying the area of coverage per
sprinkler by the number of sprinklers to be calculated (refer to the
appropriate
Installation Standard and the Authority Having Jurisdiction).
Multiply the square root of the remote area determined in the step above by
at least 1.2 and divide the product by the distance between sprinklers
on the branch lines. The quotient determines the number of sprinklers to
calculate per branch line. Any fractional sprinkler shall be carried to the
next higher whole sprinkler.

Can also get there from NFPA 13, 2007 edition 22.4.2.2.  If you have to
calculate 25 sprinklers the minimum design area is 2000 square feet (80 sq
feet minimum per sprinkler).  The number of sprinklers to calculate on a
branch line depends on the spacing pattern.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213

[email protected] wrote on 05/18/2009 06:07:02 PM:

> [image removed]
>
> Large drop sprinklers
>
> A.P.Silva
>
> to:
>
> sprinklerforum
>
> 05/18/2009 06:07 PM
>
> Sent by:
>
> [email protected]
>
> Please respond to sprinklerforum
>
> NFPA 13, 2002 table 12.3.2.2.1(a) or
> NFPA 13, 2007 table 16.2.2.1(a)
>
> Large Drop Sprinkler Design Criteria for ........Class I through Class IV
> Commodities .....
>
> Two questions:
>
> (1) Hose stream allowance for some storage configurations with dry
systems
> are given as "not applicable". Why?
> (2) Number of design sprinklers are given. But not how many on a line. I
> guess a design rectangle can be worked out, but is that the intent?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to