If the FDC and Check valve are at end of main and the check valve is near
the bottom of drop to the FDC, after a system trip (testing or for real)
would anyone remember to drain that portion of pipe that has trapped water?
My two cents worth.




Bryan A. Dann
Dannba Design Services, LLC
Fire Sprinkler Designs
Office: (740) 363-5878
Cell: (740) 803-0967
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, May 19, 2009 11:51 AM
To: [email protected]
Subject: RE: FDC for Dry Pipe Systems


I know this. But why? And how critical is it? Ron and Garth have given some
compelling reasons. Are there any other thoughts? I'd like to know why it is
being done, and how critical it is for the system.

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Arthur Tiroly
Sent: May 19, 2009 9:04 AM
To: [email protected]
Subject: RE: FDC for Dry Pipe Systems

The connection from the FDC must be below the DPV and the connection tee
must be above a swing check in the riser in most every case.

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, May 18, 2009 7:21 PM
To: [email protected]
Subject: FDC for Dry Pipe Systems

The FDC is required to be connected between the main control valve and the
dry pipe valve. I'v always thought this might be due to possible air leak
from the FDC check valve, if it's connected on the dry side, downstream of
the dry pipe valve. Is this the reason?

For a project having a single dry system, the contractor has connected the
FDC downstream of the DPV. The system seems to be holding. Any comments?

Tony 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to