If I'm not mistaken, the carpet padding takes you out of ESFR right away
because of inherent obstruction within the array (no longitudinal flues
possible).    And portable racks are a challenge to in-racks, I suppose
...    We've done probably 4 or 5 warehouses that were either dedicated
to or had significant flooring inventories, including and especially
rolled carpets and pads and all have used CM at the roof with in-racks.
One of them actually started under an ESFR system that we deconstructed
and converted back to spray sprinklers, in order to get to the in-rack
arrangement.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Tuesday, June 16, 2009 9:29 AM
To: [email protected]
Subject: RE: Carpet Pad Storage

Who is the insurance company? They would probably 
have something to say about it. I'd start there.


At 11:54 AM 6/16/2009, you wrote:

>Question: How to most effectively protect the following -
>
>*       Carpet pads (Group A plastic, expanded)
>*       Rolled and wrapped in plastic (non-encapsulated)
>*       On portable racks that are 7-feet high and 6-feet x 6-feet
square
>*       Client desires to stack them 2-high (14-feet)
>
>Building  is approximately 40-feet high (tilt 
>panel warehouse)with k-14 ESFR's calculated for 75 PSI (12 heads).
>
>The tenant space is fairly small at 30,000 
>square feet and includes some 25-foot tall 
>double-row rolled carpet racks (with in rack sprinklers per FM
criteria).
>
>Also contains some standard pallet racks with Class IV commodity to
25-feet.
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[email protected]
>
>To Unsubscribe, send an email
to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4159 (20090616) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4159 (20090616) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to