Follow NFPA requirements in the real world.  Note the requirements on
the drawings multiple times.  Tell the fitters, multiple times, properly
sloping the pipe is a "shall", not a "should".  Most of us, even here in
the south, have been involved in litigation as a result of improperly
installed dry systems.

Bobby McCullough
Atlanta Sprinkler Inspection
[email protected] 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Tuesday, June 23, 2009 1:47 PM
To: [email protected]
Subject: RE: Sloping pipe in dry pipe systems

Richard,

See NFPA 13 2007   8.16.2.3.3

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Tuesday, June 23, 2009 12:41 PM
To: sprinklerforum
Subject: Sloping pipe in dry pipe systems

I have searched but of course can not find anything that seems to answer
my
question..

In the real world, how much do you slope the pipe in a dry pipe system.
Say
you have a 100 foot run, what would you look to be the total drop over
that
run.  2", 3",  use 1/16"/ft???  Looking for your experience when trying
to
layout out a dry pipe system.

Thanks,

Richard
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to