Richard,
Usually I find there is something with the structure or trades that helps
make that decision for me when laying out. If I have to make it under X beam
at point A, and over that roof drain at point B, I can put elevations on the
drawing so that the pipe will avoid those obstructions. Section 8.16.2.3.1
thru 8.16.2.3.2 of NFPA 13 2007 gives the requirements of NFPA 13. I would
try to allow as much flexibility in the installation while meeting those
minimum pitch. 
This works out great when you have lots of room and in a perfectly level
building, however when it's crammed, it takes good communication with a good
fitter (who in turn to communicates with the other trades), about critical
height locations. 

  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Tuesday, June 23, 2009 12:41 PM
To: sprinklerforum
Subject: Sloping pipe in dry pipe systems

I have searched but of course can not find anything that seems to answer my
question..

In the real world, how much do you slope the pipe in a dry pipe system.  Say
you have a 100 foot run, what would you look to be the total drop over that
run.  2", 3",  use 1/16"/ft???  Looking for your experience when trying to
layout out a dry pipe system.

Thanks,

Richard
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to