Craig is absolutely correct. The Arch. Designs the building elements, and
then the Mech. engineer determines the heat loss/gain for each element based
upon what it is made of an how it is constructed and the location and
orientation to the sun. This includes walls, floors, ceilings, roofs,
windows and doors. They also have to input for such things as occupant load,
(Body Heat) and electrical loads (watts per SF) from lighting computers or
other heat producing equipment. They need to allow for the proper mix of
"Fresh" air (outside air) and recirculated air based upon occupancy, add in
any ventilation for things such as fume hoods or bathrooms and exhaust
hoods. Then there is the inevitable "And More".

These calculations then become the "Basis of Design" for the heating and
cooling.

More to the point, without that engineering degree, those classes in heat
transfer, and years of experience, you'd be out of luck trying this on your
own.

The simple answer is "Not MY Job!"

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, June 24, 2009 6:18 AM
To: [email protected]
Subject: RE: Heat gain/loss calculations

The mechanical/HVAC engineer or contractor does that.  An Architect would
have no clue, not their area of expertise. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay White
Sent: Tuesday, June 23, 2009 5:49 PM
To: [email protected]
Subject: Heat gain/loss calculations

Who is responsible for performing the heat gain/loss calculations in a
building?


Jay White
Estimator/Design Manager
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759
Phone: 662-324-1550
Fax:       662-324-1545
Cell:      662-312-2426


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to