I've seen two answers so far that rely on Aristotelian logic. The
first with how something operates and the second political. While both
may ultimately be correct, the tight sheetrock may act as the
escutcheon ring and the rules behind this may be political we don't
know. What we do know is that not having the escutcheon means that in
this case a part of a rated assembly is not present and that that
assembly was tested and listed with that part present. We also know
that UL is satisfied enough with the results of testing to grant this
sprinkler head a listing (I'm presuming it's a listed assembly) to put
their name on it and that the manufacturer is willing to say that if
installed properly this product will work as advertised. It may very
well work but we can't know if it's missing a part. So maybe turns
into won't function as a conservative default. As for the big, scary
government and silly rules Hud has standards and it's incumbent upon
an owner, reaping whatever benefit he gains by putting himself under
HUD oversight, to comply with those rules. I see no difference in that
than me replacing my old shake roof with composition to gain an
insurance benefit. It's their policy to charge X for shakes and Y for
comp. Or taking it to the extreme paying Ethnic Johnny every week so
"accidents" don't happen. Each level of this has decreasing government
oversight, but each level has it's own rules of engagement that I must
meet to play.

On Fri, Jul 10, 2009 at 6:55 AM, Paul Johnson<[email protected]> wrote:
> Jay,
>
> This looks like another example of our government dollars hard at work.
>
> I am not aware of anything that states a sprinkler will or will not operate
> without the escutcheon.  Maybe a manufacturer's rep would be willing to
> write a short statement explaining that while sprinklers and escutcheons are
> listed assemblies, the sprinklers will operate without the escutcheon in
> place.  Whether or not that gets the 17-point ding removed will be another
> issue.
>
> Paul Johnson
> Bardane, Inc. Visioning a competitive workforce
> (407) 401-7154 - Office
> (407) 399-5081 - Mobile
> [email protected]
> www.bardane.net
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jay Stough
> Sent: Friday, July 10, 2009 9:42 AM
> To: [email protected]
> Subject: Escutcheons
>
> I have a customer that was hit by HUD as having a sprinkler that will not
> operate because it is missing the the trim ring on a semi-recessed
> sprinkler.  They have since put one on, but the problem is they got hit with
> 17 points out of a hundred for not having a working sprinkler.  Under HUD,
> there is no re-inspection until the next time it is due.  So you take a hit
> with all other types of ratings due to this inspection.  I didn't see
> explicitely that the trim ring is required in 25, and I know it is part of a
> rated assembly from the manufacturer, but does any one have any ideas for a
> rebuttal to help get this reduced or removed as a major deficiency?  They
> can contest the finding, but replacing the trim ring does not count, you
> need to show that the sprinkler will operate.  The funny part is, in the
> picture it looks like the installing contractor did not put the escutcheon
> on because the drywall was too tight around the base ring!
>
>
>  Jay Stough
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA