I have a two thousand GPM diesel riven pump that supplies 3 large warehouses.
The test header has 4 hose connections. Inspection team tells customer that
the test header needed 4 more valves in order to do the test. Customer calls
and ask where thats written that each connection is rated for 250 gpm. NFPA 20
(2003) governs and table 5.25b says it only needs a total of 6. Am I looking
in the right spot?