I didn't reply to this because I was out of town, but I agree with Rich.
If it's configured as "one building" and the standpipe system can be
distributed internally, then a central plan configuration is consistent
with the intent of the standard.

My opinion only, etc., etc.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of R
Richardson
Sent: Wednesday, August 12, 2009 10:17 AM
To: [email protected]
Subject: Re: Multiple High Riser Towers 

Not many responses to this one.  Here is what the answer is in Seattle.

We would allow multiple high rise towers on a single property to share a
tank/pump system if the supply to each tower was NOT underground.  The
supply would have to be through a utilidor or something comparable
capable of withstanding the movement expected in an earthquake, or
through a common garage, or through the connecting breezeways etc. -
just not underground.

We allow the single pump/tank with auto fill as standard practice.
There are no requirements in the codes or NFPA for redundant fire pumps.

Regards,

Rich Richardson
Seattle Fire Department

>>> Perry Barber <[email protected]> 08/10/2009 12:14 >>>
I would like to get input on the secondary water supply requirements for

high rise buildings in seismic design category C, D, E or F.  I am 
working on a project for a hospital that has a existing patient tower 
with a secondary water supply tank and fire pump built under the 2003 
International Fire Code.

The hospital wishes to build additional high riser towers (2 more) all 
connected to the main hospital building, in essence still being one 
building. Are additional secondary water tanks and fire pumps need for 
each new high rise or can they be fed from the existing tank and pump 
and still meet the intent of the code requirement?

Also, the existing design uses a 33,000 gallon underground water tank 
and a vertical turbine pump. The tank uses float sensors to determine 
the water level within the tank and an automatic refill system from the 
city water supply.  There is not a second fire pump.

Does this meet the intent, in other words are two pumps need - one for 
the primary and one for the secondary water source?

-- 
Perry Barber
Raleigh, NC
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
For Technical Assistance, send an email to:
[email protected] 

To Unsubscribe, send an email
to:[email protected] 
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4330 (20090812) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4330 (20090812) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to