Aren't IBC semi new.  May not be any criteria.
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Jim Johnston" <[email protected]>

Date: Thu, 27 Aug 2009 09:39:07 
To: <[email protected]>
Subject: RE: NFPA 30


Craig,

I'm sorry I was in a hurry, and replied before I read your entire message.
The commodity is Mint Oil mostly a Class III-A flash point of 142 F and some
that is a Class II with 104 F Fp.  Today's standards (30- 2008) tie me to
Table 16.5.2.10 and Section 16.6.2. due to the IBC and the oil is < 1%
soluble in water according to the MSDS sheets.  This totally blows the
original system out of wack, the building was originally designed to protect
this very commodity might have been in metal IBC's though?

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Thursday, August 27, 2009 9:19 AM
To: [email protected]
Subject: RE: NFPA 30

Why foam?  It's only applicable in certain instances where you have chemical
commodities that aren't miscible or can not be controlled or suppressed with
water alone.

I don't have an NFPA 30 that far back on hand,  2000 is the oldest we've got
laying around.  But to go from a wet, tree system to a foam-water system is
not necessarily going to be one of "minimal reconfiguration".  Typically
foam-water requires less water so your hydraulics are going to need total
evaluation, plus heads may or may not be compatible with the foam-water
system so they may need to be changed out. 

There are a lot of variables need to be defined and analyzed.

Do you have the design criteria for the original? Was it actually designed
for chemical storage back then?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Thursday, August 27, 2009 12:09 PM
To: [email protected]
Subject: NFPA 30

Does anybody have a copy of NFPA 30 from 1994 or earlier era?  I have a
warehouse storing plastic IBC Totes (275 Gal) with Class II & IIIA liquids,
in double row racks - 4 levels high.  The original system was installed in
1994 by another contractor as a tree at the roof and single level of
protection in the racks, today an insurance guy would like them to protect
with foam utilizing the existing system with minimal reconfiguration,
problem is it will not calc out.  Based on 2008 NFPA 30, the original design
criteria is nowhere close to being acceptable by today's standards.

 

If anybody can help me out it would be much appreciated, please contact me
off forum.

 

Thanks,  

 

Jim Johnston, P.E.

Fire Protection Engineer

Inland Fire Protection, Inc

1100 Ahtanum Road

Yakima, WA 98903

Phone 509-248-4471 or 800-742-6156

Fax 509-248-1180

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to