Actual flow tests are the only way to get reliable data.
We are  faced with water rationing, polluting of streams by storm drain 
runoff, etc.
Modeling is becoming more prevalent.
I agree it is crap and cannot be deemed reliable.

Ed
Alpha Fire

----- Original Message ----- 
From: <[email protected]>
To: <[email protected]>
Sent: Sunday, September 06, 2009 8:24 PM
Subject: Re: NFPA 25 Proposed Routine Water Supply Testing


> Never deal woth modeling. Actual flow tests only. Most of thje modeling I 
> see is crap.
>
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: [email protected]
>
> Date: Mon, 7 Sep 2009 02:52:13
> To: <[email protected]>
> Subject: Re: NFPA 25 Proposed Routine Water Supply Testing
>
>
>
> Once a test like a flow test is commenced I'm used to the requirement to 
> continue flowing water until water is material free. On the typical casual 
> basis this is water into a styrofoam cup, until a couple grabbed samples 
> in a row show no material. Have your reading glasses on. Otherwise another 
> water system user may be negatively impacted, ie. have product ruined.
>
> A flow test uses an amazing amount of water. 50K gallons would not be 
> exceptional.
>
> Has anyone asked who is going to pay for the water? It's not free.
>
> I'm used to seeing modeling results for design. Is anyone still doing the 
> pitot routine?
>
> Yours,
>
> Bruce Verhei
>
>
>
> ----- Original Message ----- 
> From: "David de Vries" <[email protected]>
> To: [email protected]
> Sent: Thursday, September 3, 2009 9:06:48 PM GMT -08:00 US/Canada Pacific
> Subject: NFPA 25 Proposed Routine Water Supply Testing
>
> There is a proposal in NFPA 25 to require water supply testing for 
> sprinkler systems every 5 years. No trigger, like new, high-demand 
> construction in the area or deterioration in the main drain test 
> results -- just every 5 years run the test. This passed the committee on a 
> vote of 24 to 5.
>
> Anybody out there doing water supply testing for existing systems when 
> there is no indication of a deteriorated supply? Any owners asking for it?
>
> Sorry for the late heads-up. Comments on this, and all the rest of the 205 
> proposals, are due to NFPA by 5:00 p.m. EDT Friday. I will be up early to 
> prep some comments myself.
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
>
>
>
> --- 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field) 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to