I assume you are referring to assignment of the Area of Coverage and  
density.  AS Cliff indicated, how many concealed combustible spaces  
are UNOBSTRUCTED?

On a related note, the Room Design method can NOT be applied to  
concealed spaces.  This was addressed at the ROP meeting: 13-318 (and  
confirmed at the ROC meeting).  Another of those issue that are only  
known by reading the ROP/ROC.


Roland

On Sep 7, 2009, at 7:50 AM, Ralphy Henderson wrote:

>
> Can the small room provision ever apply to small isolated areas in a  
> concealed combustible space between a room's ceiling and the roof  
> deck? There is an area I'm working on that has walls sheathed to the  
> deck and was wondering if this would apply.RB
>
>
>
>