I assume you are referring to assignment of the Area of Coverage and density. AS Cliff indicated, how many concealed combustible spaces are UNOBSTRUCTED?
On a related note, the Room Design method can NOT be applied to concealed spaces. This was addressed at the ROP meeting: 13-318 (and confirmed at the ROC meeting). Another of those issue that are only known by reading the ROP/ROC. Roland On Sep 7, 2009, at 7:50 AM, Ralphy Henderson wrote: > > Can the small room provision ever apply to small isolated areas in a > concealed combustible space between a room's ceiling and the roof > deck? There is an area I'm working on that has walls sheathed to the > deck and was wondering if this would apply.RB > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)