Dave,

I didn't think the F-300 dries went that far back.All the forties  
stuff I remember were E-2 models. If the latter the big problem is the  
brass on brass inner seat. They are robust though and last a long time  
even with poor maintenance. They are 6:1 if I recall but are very  
sensitive in high water pressure situations. If it is anD-300 model  
from the forties it's a different series than i'm thinking of and I'll  
be of no help.

[email protected]
Sent from my iPhone

Ron Greenman
...On the phone

On Sep 12, 2009, at 2:46 PM, "Dave Phelan" <[email protected]> wrote:

> Greetings to all -
>
>
>
> I am working on a project with several 1940 era Grinnell F-300 DPV's  
> - 4
> inch.  One of the many issues with these systems is the incorrect air
> settings from the supplied air system and lack of proper air  
> maintenance
> devices.  Does anyone have a table or air pressure / trip point  
> information
> on these valves?
>
>
>
> The systems are holding back a fire pump which develops 180 PSI at  
> churn and
> maintains 125 PSI via the jockey pump.  Currently they are providing  
> up to
> 80 PSI of air in the systems .. Did I mention there were some  
> problems with
> this project ?
>
>
>
>
>
> Dave P.
>
> An AHJ in NJ
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to