tough to say, as I don't
have a complete picture,
but I am sure about feeling stronger
over an ounce
of prevention
versus a pound of cure.

Personally, I would double or treble the
NFPA 11 RDD for the entire covered area.
Another approach is to double the quantity.
Even if you extinguish the fire before
going into extra innings with your foam,

we still we need that foam for control of the fire
AFTER it is extinguished.  Cool down and suppression
of vapors during mop-up.

Furthermore, if the fire involved any significant
spilling or spraying liquid, the odds are good that
foam alone is not going to allow your response
teams to go straight home.  Bring a shot of Purple-K
along with you too.  Load the dry-chem for several
8 lb/sec discharges for 5 second durations.  There
are some excellent tools for putting
this dry chemical right where you want it, and it
is fired simultaneous with the foam.  Works wonders
on overturned tankers at roadway disasters, too.

12,000 gallons of Class II liquids may not be
in the same strategic ballpark as a 4 million
gallon tank of the same, but without the right tools,
a fire in a 12,000 gallon tanker still will
make me look like the fool who was sleeping
in school.


scot deal
Excelsior Fire Engineering



updated their loading rack cover for tanker trucks, the old rack has a foam
fire protection system.  The facility did not remove the old smaller rack
partial rack cover or upgrade the foam system.  will this cause fire
protection problems.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to