In NFPA 13 that term is only used with regards to support of piping.

BUT, a cushion or safety factor can be mandated by the AHJ and it can vary.

I've seen requirements for 10% or 10psi off your tested residual and Static, 
10% off just the residual, 15% difference between demand and actual available, 
it runs the gamut.  

Everyone probably has a number they use of what they feel safe with.  There are 
factors that often weigh into that number.

First check with the AHJ or Underwriter to see if they have a requirement. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Karen Purvis
Sent: Wednesday, September 23, 2009 2:47 PM
To: [email protected]
Subject: Safety factor

Can anyone tell me, does NFPA 13 or 14 say anything about a particular safety 
factor to be used in the hydraulic calculations?

 

Karen Purvis

Senior Designer

Facility Systems Consultants

713 South Central Street,

Suite 101

Knoxville, TN 37902

ph.865-246-0164

fax 865-246-1084

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to