The accelerator is tripping then of course the dry pipe trips.

On Thu, Sep 24, 2009 at 6:55 PM, Ed Vining <[email protected]> wrote:

> What trips the properly operating accelerator is the rate of pressure drop,
> rather the pressure drop in numbers.  If it trips on a slow drop of 0.5
> psi,
> it is at least in need of a good cleaning.  If you opened the inspectors
> test and it tripped on that drop, maybe it is working properly.
>
> If you do decide to replace it, consider an electronic accelerator.
>
> Ed Vining
>
> On Thu, Sep 24, 2009 at 6:48 PM, Forest Wilson <[email protected]
> >wrote:
>
> > What does the valve trip without the accelerator?
> >
> >
> > Forest Wilson
> >
> > Project Manager
> > Cherokee Fire Protection Co.
> > 3195 Dayton Xenia Rd Ste 900
> > Dayton OH 45434
> >
> > ph: 937-376-2333
> > fx: 614-455-4324
> > cell: 937-307-5647
> >
> >
> > .
> >
> >
> >
> > Visit our blog: www.cherokee-fire.blogspot.com
> >
> >
> >
> >
> >
> >
> >
> > NOTICE: The information contained in this email is intended to be
> > solely for the use of the named individual or entity to which it is
> > directed and may contain information that is privileged or otherwise
> > confidential. It is not intended for transmission to, or receipt by,
> > anyone other than the named addressee (or a person authorized to
> > deliver it to the named addressee). It should not be copied or
> > forwarded to any unauthorized persons. If you have received this
> > electronic mail transmission in error, please delete it from your
> > system without copying or forwarding it, and notify the sender of the
> > error by reply email or by calling Cherokee Fire Protection Co. at
> > 888-347-3079 toll free.
> >
> >
> > -----Original Message-----
> > From: ETHER BARLOW <[email protected]>
> > To: sprinklerforum <[email protected]>
> > Sent: Thu, 24 Sep 2009 18:43:48 -0700
> > Subject: 10 yr old accelerator
> >
> > We have a facility that is 10 yrs. old and it has a CENTRAL Dry Pipe
> > valve
> > Installed with a Central "Model A" Accelerator. The dry vale is tripping
> > with only .5 psi pressure drop. Does the accelerator have an adjustment
> > or
> > is it just a bad one that needs to be replaced.
> >
> > --
> > My Thanks to You!
> >
> > Ether J. Barlow
> > Cell 702-375-1228
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > (Put the word unsubscribe in the subject field)
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ed Vining
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
>  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
My Thanks to You!

Ether J. Barlow
Cell 702-375-1228
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to