Woops, I left out the than.   "rather THAN the pressure drop in numbers."

Is the owner getting accidental tripping?

Ed



On Thu, Sep 24, 2009 at 7:02 PM, ETHER BARLOW <[email protected]> wrote:

> The accelerator is tripping then of course the dry pipe trips.
>
> On Thu, Sep 24, 2009 at 6:55 PM, Ed Vining <[email protected]> wrote:
>
> > What trips the properly operating accelerator is the rate of pressure
> drop,
> > rather the pressure drop in numbers.  If it trips on a slow drop of 0.5
> > psi,
> > it is at least in need of a good cleaning.  If you opened the inspectors
> > test and it tripped on that drop, maybe it is working properly.
> >
> > If you do decide to replace it, consider an electronic accelerator.
> >
> > Ed Vining
> >
> > On Thu, Sep 24, 2009 at 6:48 PM, Forest Wilson <[email protected]
> > >wrote:
> >
> > > What does the valve trip without the accelerator?
> > >
> > >
> > > Forest Wilson
> > >
> > > Project Manager
> > > Cherokee Fire Protection Co.
> > > 3195 Dayton Xenia Rd Ste 900
> > > Dayton OH 45434
> > >
> > > ph: 937-376-2333
> > > fx: 614-455-4324
> > > cell: 937-307-5647
> > >
> > >
> > > .
> > >
>
-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to