I have been asked a question by a facility owner, as to if they could conduct 
monthly in service pump checks rather then the NFPA 25 required weekly test as 
outlined:

The question is of unique note in that this facility has been conducting the 
required weekly test for over 15 years.  (We have the witnessed test records - 
by fire marshal)
It begs to the underlying question of,  is the code to demanding? the pump and 
motor have had problems over the years; shaft alignment, bearings worn, relief 
valves having to be replaced. The pump and motor are the original installed in 
1977. The facility operator is concerned that the pump/motor is wearing out?  
We also have witnessed annual fire pump tests record and the pump had to be 
rebuilt a few years back.  Water supply strainer replaced and so on with minor 
problems.  I would dare to say that this record is fairly complete with 
information.  The pump is showing signs of a lower output but still meeting 
required flow output.



8.3*<http://nfpacodesonline.org/a/c.ref/ID00002503929/sec> 
Testing.<javascript:void(0)><javascript:void(0)><javascript:void(0)>

8.3.1   A weekly test of fire pump assemblies shall be conducted without 
flowing water.


8.3.1.1   The weekly test shall be conducted by starting the pump automatically.



8.3.1.2   The electric pump shall run a minimum of 10 minutes.



8.3.1.3   The diesel pump shall run a minimum of 30 minutes.



8.3.1.4   A valve installed to open as a safety feature shall be permitted to 
discharge water.



8.3.1.5   The automatic weekly test timer shall be permitted to be substituted 
for the starting procedure.




8.3.2 Weekly Tests.

8.3.2.1   Qualified operating personnel shall be in attendance during the 
weekly pump operation.



8.3.2.2*<http://nfpacodesonline.org/a/c.ref/ID00002503946/sec>   The pertinent 
visual observations or adjustments specified in the following checklists shall 
be conducted while the pump is running:


 *
(1)
Pump system procedure:

    *
(a)
Record the system suction and discharge pressure gauge readings.
    *
(b)
Check the pump packing glands for slight discharge.
    *
(c)
Adjust gland nuts if necessary.
    *
(d)
Check for unusual noise or vibration.
    *
(e)
Check packing boxes, bearings, or pump casing for overheating.
    *
(f)
Record the pump starting pressure.

 *
(2)
Electrical system procedure:

    *
(a)
Observe the time for motor to accelerate to full speed.
    *
(b)
Record the time controller is on first step (for reduced voltage or reduced 
current starting).
    *
(c)
Record the time pump runs after starting (for automatic stop controllers).


________________________________
FOIA Disclaimer
You are hereby advised that, pursuant to the Virginia Freedom of Information 
Act, written correspondence (including, but not limited to, letters, e-mails 
and faxes) from and to the City of Fairfax and its officials and employees, and 
others acting on its behalf, may be subject to disclosure as being a public 
record. This includes the e-mail address(es) and other contact and identifying 
information for parties involved in the correspondence.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to