If an opinion is requested, considering the situation I would tend to
support it.
I have several clients I've given instructions to, placed directional
signage, given logbooks to, who do it monthly.
I look at it as it's better than nothing, or a start.  I always tell them of
the code requirements and to talk to the AHJ and their insurer.
I would never pass judgment or waive a requirement.  Some have only one guy,
little funds, etc., and I look at it as a step in the right direction.
What happened the 15 years before they started weekly tests?
Tom


I have been asked a question by a facility owner, as to if they could
conduct monthly in service pump checks rather then the NFPA 25 required
weekly test as outlined:

The question is of unique note in that this facility has been conducting the
required weekly test for over 15 years.  (We have the witnessed test records
- by fire marshal)
It begs to the underlying question of,  is the code to demanding? the pump
and motor have had problems over the years; shaft alignment, bearings worn,
relief valves having to be replaced. The pump and motor are the original
installed in 1977. The facility operator is concerned that the pump/motor is
wearing out?  We also have witnessed annual fire pump tests record and the
pump had to be rebuilt a few years back.  Water supply strainer replaced and
so on with minor problems.  I would dare to say that this record is fairly
complete with information.  The pump is showing signs of a lower output but
still meeting required flow output.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to