We have a hotel designed per NFPA 13.  The 2nd floor is concrete.  The
building plans showed the gyp board ceilings to be framed with non
combustible channel.  Therefore, the space above the 1st floor ceilings
would be a non-combustible concealed space.  However, when the fitters
arrived on site, it was found that the GC has taken it upon himself to frame
all of the gyp board ceilings / soffits on the first floor with wood.  Would
this be considered minimal / minor quantities of non structural wood?  What
is a decent defining factor for minor quantities?  If sprinklers are
required, the GC realized today that a change order is forth-coming.  It is
just an issue of scheduling to go back and get the first floor redesigned to
accomodate the new construction.  This project was also done with CPVC
piping, so we would have to go with the specially listed concealed space
sprinklers to protect these areas.
 
8.15.1.2.1*  Concealed spaces of noncombustible and limited-combustible
construction with minimal combustible loading having no access shall not
require sprinkler protection. The space shall be considered a concealed
space even with small openings such as those used as return air for a
plenum. (For additional information on combustible loading, see
A.8.15.1.2.1.)
 
A.8.15.1.2.1  Minor quantities of combustible materials such as but not
limited to: cabling, nonmetallic plumbing piping, non-structural wood, etc.
can be present in concealed spaces constructed of limited or noncombustible
materials but should not typically be viewed as requiring sprinklers (see
8.15.1.1). For example, it is not the intent of this section to require
sprinklers, which would not otherwise be required, in the interstitial space
of a typical office building solely due to the presence of the usual amount
of cabling within the space.  The threshold value at which sprinklers become
necessary in the concealed space is not defined.
 
Thanks in advance for any help / opinions.
 
Travis Mack
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to