There are lots of construction types that cannot be sprinklered in accordance with NFPA #13, at least not at a reasonable cost. Ever seen a building containing more than 12 ft high storage that has a roof pitch greater than 2/12? A couple of scenarios I have seen that don't fit into a convenient NFPA definition are 30" deep concrete tees with the stems less than 3 ft on center and 16" deep open web wood trusses 12" on center.
Unusual types of construction more likely require sprinkler modifications than building modifications. Ron Fletcher Aero Automatic Phoenix -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Thursday, October 01, 2009 5:24 AM To: [email protected]; [email protected] Subject: RE: A.8.15.1.2.1 Have you looked at the new data for the 36" or less concealed spaces with the specially listed heads? The only place in 13 that I am aware of that forces a BUILDING modification? I think that is very poor practice to start. Greg McGahan Operations Manager Living Water Fire Protection 1160 McKenzie Road P.O. Box 877 Cantonment, Florida 32533 (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Travis Mack Sent: Wednesday, September 30, 2009 4:21 PM To: [email protected] Subject: RE: A.8.15.1.2.1 Yeah. This is one of those that "I can't define it, but I know it when I see it" things. My feeling is that it is going to need sprinklers. I haven't seen the space yet, just what the fitter and project manager relayed today. Anyway, the rooms are like a typical Holiday Inn 1st floor: conference rooms, offices, etc. The gyp goes to the deck in all of the rooms for the walls, so that is not an issue. For example, a conference room is 20x40. It has a 3' soffit at the perimeter that is framed in wood (2x4 @ 16" on center) to create the soffit. Does that qualify as minor combustibles? Not sure, but I don't want to make the judgment call. That is above my pay grade. We just realized another issue. The bottom of the concrete deck is 13'-8". This ceiling is at 10'-0". This exceeds the 36" max dimension allowed for the specially listed concealed space sprinklers. So, all of the piping would have to go to steel and use standard spray sprinklers. The project is turning into Pandora's box. I am not fully sure if the specially listed concealed space sprinklers could even be used in this application if it met the 36" requirement. I have to research that a bit more. > I agree with Todd if it's the walls = sprinkler all. > > But I think the question is limited to gyp CIELINGS and SOFFITS. In that > case I think '02-8.14.1.5 can help, Localized Protection of Exposed > Combustible Construction. > > I do think you have to deal with it either way. Unless the area involved > is > really, really small like a few sq.ft. separated by 20's of feet to the > next > few sq.ft. IDK? Without seeing it can't advise on the judgment call on > how > small is small. > > > > Chris Cahill, P.E. > Fire Protection Engineer > Sentry Fire Protection, Inc. > > 763-658-4483 > 763-658-4921 fax > > Email: [email protected] > > Mail: P.O. Box 69 > Waverly, MN 55390 > > Location: 4439 Hwy 12 SW > Waverly, MN 55390 > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Todd > Williams > Sent: Wednesday, September 30, 2009 3:03 PM > To: [email protected] > Subject: Re: A.8.15.1.2.1 > > Travis, > > I've always looked at "limited combustible" as a subjective term. You > know what isn't, but not sure what is. If you have 2x's at 16" oc all > over the place, chances are it isn't "limited combustible". If they > used a few pieces of wood to support and ceiling fixture in an > otherwise N/C space, that would be limited. I usually work with the > AHJ to come up with a consensus. That also stops a lot of arguments. > > Todd > > At 03:10 PM 9/30/2009, you wrote: >>We have a hotel designed per NFPA 13. The 2nd floor is concrete. The >>building plans showed the gyp board ceilings to be framed with non >>combustible channel. Therefore, the space above the 1st floor ceilings >>would be a non-combustible concealed space. However, when the fitters >>arrived on site, it was found that the GC has taken it upon himself to > frame >>all of the gyp board ceilings / soffits on the first floor with wood. > Would >>this be considered minimal / minor quantities of non structural wood? >> What >>is a decent defining factor for minor quantities? If sprinklers are >>required, the GC realized today that a change order is forth-coming. It >> is >>just an issue of scheduling to go back and get the first floor redesigned > to >>accomodate the new construction. This project was also done with CPVC >>piping, so we would have to go with the specially listed concealed space >>sprinklers to protect these areas. >> >>8.15.1.2.1* Concealed spaces of noncombustible and limited-combustible >>construction with minimal combustible loading having no access shall not >>require sprinkler protection. The space shall be considered a concealed >>space even with small openings such as those used as return air for a >>plenum. (For additional information on combustible loading, see >>A.8.15.1.2.1.) >> >>A.8.15.1.2.1 Minor quantities of combustible materials such as but not >>limited to: cabling, nonmetallic plumbing piping, non-structural wood, >> etc. >>can be present in concealed spaces constructed of limited or >> noncombustible >>materials but should not typically be viewed as requiring sprinklers (see >>8.15.1.1). For example, it is not the intent of this section to require >>sprinklers, which would not otherwise be required, in the interstitial > space >>of a typical office building solely due to the presence of the usual >> amount >>of cabling within the space. The threshold value at which sprinklers > become >>necessary in the concealed space is not defined. >> >>Thanks in advance for any help / opinions. >> >>Travis Mack >>_______________________________________________ >>Sprinklerforum mailing list >>[email protected] >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >>For Technical Assistance, send an email to: [email protected] >> >>To Unsubscribe, send an email to:[email protected] >>(Put the word unsubscribe in the subject field) > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)