I don't know what they have so can't comment specifically.  

>From the do's and don'ts from Blazemaster:

In bold face - WARNING: AIR OR COMPRESSED GAS MUST NEVER BE USED FOR
PRESSURE TESTING 

And normal text -

Fill lines slowly and bleed the air from the system prior to pressure
testing.  

And -

After cut-in cure times are met, the system must be slowly filled with water
and the air bled from the furthest and highest sprinkler heads before test
pressure is applied (refer to manufacturer's installation instructions
regarding Hydrostatic Testing). 

And -

After cut-in cure times are met and the air is bled from the system, it is
recommended that portion of the sprinkler system containing the cut-in tee
be pressure tested. Prior to pressure testing, the system must be sectioned
off to its smallest area using floor valves, etc., to isolate the cut-in
area. It is further recommended that the test pressure applied should not
exceed 50 psi over the system pressure. This approach will minimize the
potential for water damage should a leak occur.

That's rather clear to me TESTING!  I don't see anything related to normal
return to service after whatever.  13 would not normally require a new test
for some add and relocates as I'm guessing was the scope of work.  So not
testing would be code compliant in this case.  Again I would bet fitters in
the field rarely if ever bleed the air for testing on new systems.  Wrong?
Technically.  Sure they don't fill and pressurize with air they know to use
water.  Although I do know some fitters will put 20-30psi of air on the
system to make sure it's holding before they fill with water.   Of course I
asked what good knowing it was leaking did them if they couldn't see air
leaks and most likely could hear them either.  Yeah, well ummmmmm.....ya
see....  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: Bill Brooks [mailto:[email protected]] 
Sent: Wednesday, October 28, 2009 8:32 AM
To: [email protected]
Subject: RE: Homeowner needs advice

Chris,

I like your response but could you discuss (via the forum) the product spec
sheet issue raised by the homeowner.  If removing the air doesn't matter,
why does the spec sheet highlight it?  Is this only applicable to the
initial hydrostatic test?  I think this would close the loop for the
homeowner.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, October 28, 2009 9:21 AM
To: [email protected]
Subject: RE: Homeowner needs advice

I think Ed confused the issue.  He's not wrong but I don't see it as
applicable.  Hydrostatic testing is not the question.  The bleeding of air
for test purposes is recommended because yes it will create a serious hazard
if it ruptures.  I'd venture though this bleeding is not actually done in
the field. This testing is done at 200 psi.  Your system most likely does
not have this kind of pressure on it.  And even if it did most of what is in
the system is water not air.   

Air is compressible, water is not for these purposes. This is why air at
pressure is dangerous and water not as much.  The volume of the air is also
a critical factor.  A little air at very high pressure is not as big an
issue as a lot of air at a lower pressure.  Think when air is compressed
energy is retained.  The more volume of air, the higher the pressure the
more retained energy.  When the pipe breaks this energy is released.  The
water not being compressible does not retain as much energy.    

There is no reason really to bleed the air in the situation described.
Actually some air in the system is a good thing.  Because it is compressible
is "absorbs" temperature changes and pressure surges much, much better than
water.  Think of it like a spring.  If there was no air in the system and
the temperature rose just a few degrees the pipe would break.  This is the
ratio of Pressure = Temperature from basic science.

Taking an empty system at 0 pressure and filling it with water at street
pressure leaves the air in the system, true.  But after it's compressed to
street pressure (much <200 psi, probably in the 80 range) there is very
little volume left.  Recall the ratio of Pressure * Volume = a steady value
with no changes to Temperature from basic science.  Double the pressure =
1/2 the volume.  With average street pressure you are doubling the pressure
many, many times.

If one suspects trapped air is causing false alarms like George suggested
the real problem is a leaking check valve.  Each time the system surges from
the city supply the new high pressure should be locked in.  This could take
a couple hours to a couple days to stabilize at the highest pressure.  But
at least in these parts surges in the street are not that common on scale or
duration to cause false alarms.  
 
Again there is no reason to bleed the air in your situation.
  
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, October 27, 2009 6:41 PM
To: [email protected]
Subject: Homeowner needs advice

I'm not sure how this email forum works.  I'm sending this out blind 
hoping one of you pros has some advice for me.

I am a homeowner in a three-story townhouse.  Recently, a company did 
some minor modification to our fire sprinkler system - moving a 
couple of heads for a basement remodel.  When they were done with the 
pipe and heads, they simply re-pressurized the system without 
bleeding out the air trapped in the lines.  From what little I know 
about it, I thought this step was very important to eliminate any 
pressurize air in the system and preventing dangerous surge 
pressures.  It says so in big bold type on the product spec sheet for 
the CPVC pipe.  When I asked the installer he said they don't need to 
bleed it, but couldn't explain why not.

Before I go raising a stink about it, I want to know if your forum 
agrees that it's not necessary; or do I need to pester them into 
doing it correctly.

Thanks.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to